This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Hotspare LM without KNX connection (Over LAN)
#1
Hello,

I have 2 pcs LM Re:actor 3 devices at site. KNX connection between LM not used. LM are connected over LAN.

How to make one LM to be main device other to be slave?? And if probrem appeared, what can I solve?? Slave LM will take all function of main device? Can I somehow show problem on visualisation - at example that slave LM now is used? How quick slave device will takes all functions of main in case of problems?? May be you can advice me something and describe configuration more in detail, becouse I am novice with LM now...

Alex
Reply
#2
(13.06.2017, 10:09)AlexLV Wrote: Hello,

I have 2 pcs LM Re:actor 3 devices at site. KNX connection between LM not used. LM are connected over LAN.

How to make one LM to be main device other to be slave?? And if probrem appeared, what can I solve?? Slave LM will take all function of main device? Can I somehow show problem on visualisation - at example that slave LM now is used? How quick slave device will takes all functions of main in case of problems?? May be you can advice me something and describe configuration more in detail, becouse I am novice with LM now...

Alex

Hi, maybe this example could help you http://openrb.com/master-slave-logicmachine/
Reply
#3
Thank you , but in my case KNX bus totally not used. I have 2 LM connected over LAN - they are in one subnet. May be I can somehow use ping command instead using KNX bus? I have no KNX power supply in my project.. Sad
Reply
#4
Hi,

You don't need a knx power supply to use KNX IP.

So the devices should be able to send KNX telegrams to another.

You also need to build some custom javascript to redirect the visu from master to slave so you can show status of master and slave and keep control options.

I have done it before so it is possible (:

BR,

Erwin
Reply
#5
[quote pid='4854' dateline='1497384727']
Thank you Ervin,

may be you can write for me a little more details how to configure my devices? Also not clearly understand about visualisation.. For example - my phone connect directly to main device. If it is not available, how to reconnect to slave?? Or it will be done automatically with script?? If main device will be back - what about synchronisation?
[/quote]
Reply
#6
Hi,

To make KNX IP working between the controllers do the following on both of them:

Utilities -> System -> Network -> Knx Connection -> Set mode to: EIBnet/IP routing, set KNX address to 1.1.1 on first controller and 1.1.2 on second controller and check KNX IP features on both controllers (enabled), click 'OK' and click 'Apply Changes' in the right upper corner (red button) to apply the changes.

Create in both controllers a obect 1/1/1 and write a value in one of them. The same value should be set in the second controller. Now your KNX IP is working.

For redundant setup check our application note:

http://www.schneider-electric.com/en/dow.../AN023_SL/

Use something like this custom JavaScript to redirect the client to your slave controller visu when websocket is disconnected.

Code:
$(function() {
 var counter = 0;
  if (typeof localbus !== 'undefined') {
    setInterval(function() {
      if (!!localbus.ws == false){
         counter = counter + 1;
       if (counter > 3){
           $(location).attr('href', 'http://admin:admin@192.168.0.12/scada-vis')
       }
     } else {
       counter = 0;
     }
    }, 1000);
  }
});

Or use something like this custom JavaScript to redirect the client to your slave controller visu when url cannot be reached.

Code:
$(function() {
 var counter = 0;
 function ping(){
    $.ajax({
       url: 'http://192.168.0.11/scada/vis',
       success: function(result){
          counter = 0;
       },    
       error: function(result){
          counter = counter + 1;
          if (counter > 3){
             $(location).attr('href', 'http://admin:admin@192.168.0.12/scada-vis')
          }
       }
    });
 }
 setInterval(function() {
    ping();
  }, 5000);
});
BR,

Erwin