Hi
I suddenly get modbus operation timed out. Earlier it came occationaly but now it stopped and gives error log, so no modbus communicatiin in a month. Any ideas?
I have the same problem, with the UIO20 side by side to the LogicMachine, it does not respond either the RTU scan or the RTU read test, same with other modbus devices,
in other LogicMachines I have tried it and same thing happens, all of them are running 20170601 firmware
Then it means that modbus is working. If you change serial port settings (baud rate / parity / stop bits), you have to do the addressing again, otherwise UIO20 will still be using old settings.
(20.06.2017, 09:40)admin Wrote: Then it means that modbus is working. If you change serial port settings (baud rate / parity / stop bits), you have to do the addressing again, otherwise UIO20 will still be using old settings.
I was wrong.. the Write Address is not working either, its like the Modbus is not working at all...
Hi
Now i got modbus timeout on another project with 2 rtu slaves and 2 tcp slaves. Much communication goes without erroes but sometimes there comes error messages in log.
Running a spacelynk on this project. Any ideas how to find out why? Modbus mapper user with profiles
I have the same problem. Operation timed out.
As for the baud rate, addresses and cables i am sure that everything is ok because before LM i had another modbus master (txi2.open) and everything was ok.
How i can change the scan delay time or the telegram delay?