Using LM4 here, done integration and programming with KNX bus. But, when using from touch visualisation; at first time difference between triggering of events and clicking the action were 15-20 seconds . Then, one of the light circuit started automatically with 100% and 20% sometimes; which was then stuck into infinite loop until KNX TP was removed from LM4. What could be the issue here?
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
Check that you don't have scripts which are causing infinite loops. Do you have any other KNX/IP routers/gateways connected to the same KNX/TP line as your LM4?
Posts: 24
Threads: 9
Joined: Jan 2016
Reputation:
1
No scripts.
But other KNX/IP router was connected to same KNX/TP line. After disconnecting it, touch visualisation was smooth.
Thank you.
Posts: 24
Threads: 9
Joined: Jan 2016
Reputation:
1
How KNX can be connected to LM-Ambient?
As it works as KNX/IP router, so how it communicates with KNX TP lines?
Posts: 7758
Threads: 42
Joined: Jun 2015
Reputation:
447
You can use any KNX/TP router/gateway or LM4. For gateway you can set Ambient to connect to it via tunneling, otherwise it will use routing and should work without any extra configuration.