AHU MODBUS TCP VALUE
Hi, I try to connect to Schneider-electric Homelynx and get the airflow from an IVP AHU ventilation unit with a climactix controller.
I need to compare two values in order to control a mixing valve.
The valve opens and closes until the two values are as equal as possible.
The value is to be retrieved from a Holding register with the address 4x0055 and 4x0056.
But unfortunately I do not get any values, it seems that it does not connect or I have typed the wrong code to get the air value correctly.
require('luamodbus')
if not mb then
   mb = luamodbus.tcp()
   mb:open('192.168.201.53')
   mb:connect()
mb:setdebug(true)
openvalue =  grp.getvalue('6/3/1')
tfvalue = mb:readinputregisters(54)
ffvalue = mb:readinputregisters(55)
mb:close()
if tfvalue > ffvalue then
 if openvalue < 220 then
   openvalue = openvalue + 25
if ffvalue < ffvalue then
 if openvalue > 25 then
   openvalue = openvalue - 25
grp.write('6/3/1', openvalue)
I would be very grateful if you can help me with this problem
/Tommy
First of all you have not set a port on the Modbus TCP connection:
mb:open('192.168.201.53', 502)
Try also:
tfvalue, ffvalue = mb:readregisters(55, 2)
log(tfvalue,ffvalue)
If that does not work try changing 55 to 54
(01.11.2018, 19:42)Elmyran Wrote: Hi, I try to connect to Schneider-electric Homelynx and get the airflow from an IVP AHU ventilation unit with a climactix controller.
if not mb then
   mb:connect()
mb:setdebug(true)
mb:close()
/Tommy
Hi Tommy,
To establish modbus TCP connection between modbus master and modbus slave, you need to specify the port and the slave Id.
B.R,
Chouaibou.
Not 100% sure but i believe slave id is optional by TCP device (without it the default is used).
Is it a resident or a scheduled script? If it's resident then it will only work once because you are closing the connection via mb:close(). Setting slave id for TCP is optional by standard (255 is used when not set) but some devices might require it.
Start by logging each step return results:
local mb = luamodbus.tcp()
local res, err = mb:open('192.168.201.53')
log('open', res, err)
local res, err = mb:connect()
log('connect', res, err)
local res, err = mb:readinputregisters(54)
log('read', res, err)
mb:close()
Thanks for your help, I got the script to work today. When I contacted AHU, I realized that it was the wrong values I received. There were inputs 95 and 96 that I needed to compare.
Here is the final working code:
if not mb then
   mb:connect()
openvalue =  grp.getvalue('6/3/1', dt.uint8)
tfvalue = mb:readinputregisters(94, dt.uint16) -- 3x0095 Supply air flow
ffvalue = mb:readinputregisters(95, dt.uint16) -- 3x0096 Exhaust air flow
if tfvalue and ffvalue == 0 then
  openvalue = 0
if tfvalue < ffvalue then
grp.write('6/3/1', openvalue, dt.int8)
it was as simple as that. Big Grin