temperature not reach setpoint
Hy,
Maybe is same example script.
I need script if real temperature difference is more then 1 degree of set point in 24 hours need to send alert.
You need two scripts:
1. Event script mapped to a tag (for both setpoint and current temperature). For each object update, check if delta is within limits or not. If delta is ok, put current timestamp in storage:
temp =  grp.getvalue('1/1/1') setp = grp.getvalue('1/1/2') delta = math.abs(temp - setp) if delta <= 1 then   storage.set('last_update', os.time())   storage.set('notified', false) end
2. Scheduled script which will check time difference between now and last_update key (in seconds):
prev = storage.get('last_update', 0) delta = prev - os.time() if delta >= (24 * 60 * 60) then   notified = storage.get('notified')   if not notified then     -- send e-mail here     storage.set('notified', true)   end end