This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Peak load limiter
#10
Hi,

Here is a more complex script for load balancing, i use it for EV chargers, they can use max 63 Amp and need minimal 8 Amp, based on active chargers and available power the chargers are set to a maximum loader output over modbus (for our EVLink)

All works with TAG's on the binary state (active/not active) object and a offset of 1 in the main address (32/1/1 = State -> 32/1/1 = Set max charging output) so you can easily add multiple chargers (:
Code:
-- Get maximal available amperage
Max_Amp = grp.getvalue('35/0/10')

-- Get current messured amperage
Current_Amp = grp.getvalue('35/0/11')

-- Calculate available amperage for loaders
Available_Amp = Max_Amp - Current_Amp

-- Minimal amperage output on loader
Min_Loader_Amp = 8

-- Maximal amperage output on loader
Max_Loader_Amp = 63

-- Get all loaders on/off states
All_Loaders = grp.tag('LoaderState')

-- Function to sort table by updatetime
local function tableSortCat (a,b)
 return a.updatetime < b.updatetime
end

-- Sort table All_Loaders by updatetime
table.sort(All_Loaders, tableSortCat)

-- Create table with active loader
Active_Loaders = {}

-- Determine amount of active loaders
Number_Active_Loaders = 0

-- Ceeate new table with values and only loader tagged bit objects
for _, item in pairs(All_Loaders) do
 if item.datatype == 1 or (item.datatype > 999 and item.datatype < 2000) then
   if item.value == true then
     Number_Active_Loaders = Number_Active_Loaders + 1
   end
   table.insert(Active_Loaders, {id = item.id, updatetime = item.updatetime, datatype = item.datatype, address = item.address, value = item.value})
 end
end

-- Sort table Active_Loaders by updatetime
table.sort(Active_Loaders, tableSortCat)

-- Determine maximum loaders based on available power
Max_Number_Loaders_Possible =  math.floor(Available_Amp / Min_Loader_Amp)

-- Check if more loaders are active then max possible loaders
if Number_Active_Loaders < Max_Number_Loaders_Possible then
 Max_Number_Loaders_Possible = Number_Active_Loaders
end

--Set available amperage per loader
Available_Amperage_Loader_Per_Unit = math.round(Available_Amp / Max_Number_Loaders_Possible, 2)

--Check if output exceeds loaders Max_Amp
if Available_Amperage_Loader_Per_Unit > Max_Loader_Amp then
 Available_Amperage_Loader_Per_Unit = Max_Loader_Amp
end

-- Set loaders to 0 when current amperage exceeds max amperage
if Current_Amp > Max_Amp then
    Max_Number_Loaders_Possible = 0
 Available_Amperage_Loader_Per_Unit = 0
end

-- Write values to the output of each loader
Number_Loaders_Value_Written = 0
for _, item in pairs(All_Loaders) do
 Address_Table = string.split(item.address, "/")
 New_Address = Address_Table[1]+1 .. '/' .. Address_Table[2] .. '/' .. Address_Table[3]
 if item.value == true then
   if Number_Loaders_Value_Written < Max_Number_Loaders_Possible then
       grp.checkupdate(New_Address,Available_Amperage_Loader_Per_Unit)
     Number_Loaders_Value_Written = Number_Loaders_Value_Written + 1
   else
     grp.checkupdate(New_Address,0)
   end
 else
   grp.checkupdate(New_Address,0)
 end
end
BR,

Erwin
Reply


Messages In This Thread
Peak load limiter - by tomnord - 07.12.2018, 15:41
RE: Peak load limiter - by buuuudzik - 07.12.2018, 17:13
RE: Peak load limiter - by tomnord - 07.12.2018, 21:25
RE: Peak load limiter - by Domoticatorino - 10.12.2018, 17:14
RE: Peak load limiter - by Domoticatorino - 12.12.2018, 20:09
RE: Peak load limiter - by Erwin van der Zwart - 12.12.2018, 22:45
RE: Peak load limiter - by BMA - 19.02.2021, 17:11
RE: Peak load limiter - by tomnord - 08.12.2018, 18:33

Forum Jump: