Remaining time or counter
I am wondering if there could be a possibility to get a timer working. Its a client that want to visualize the staircase timer.
So like a clock or something else to count the time remaining.
with value from the detector triggers the count down and new "1" retriggers the remaining time?
Any one got any ideas?
This is an old script i created when i was learning LUA so probably can be improved (:
-- ** Staircase logic with external time object and retriggering on input object Version 3.1 ** --
-- ****************************** Created by Erwin van der Zwart **************************** --
-- ************************************** SET PARAMETERS ************************************ --
-- Set input address
AddressInput = '6/0/0'
-- Set output address
AddressOutput = '6/0/1'
-- Set external time address (optional)
AddressExternalTime = '6/0/2'
-- Use time left indication
UseTimeLeft = true -- Set to false if no time left indication is used
-- Set feedback adress of time left indication (optional)
AddressTimeLeft = '6/0/3'
-- Set time delay (Used when external time is not available)
SetDelay = 10
-- Seconds or Minutes
SetSec = true -- Set to false for Minutes
-- Set factor delay (Multiplies Delay)
SetFac = 1
-- Set unique name for staircase timer (to avoid same storage name usage)
StaircaseName = 'Staircase_1'
-- Logic can be turned of by value 0
Off_by_Value_Zero = false
-- ************************************** END PARAMETERS ************************************ --
-- *************************** DON'T CHANGE ANYTHING UNDER THIS LINE ************************ --
inputvalue = event.getvalue
if Off_by_Value_Zero == false and (event.getvalue() == false or event.getvalue() == 0) then
 -- Exit script
 return
ValueInput = grp.getvalue(AddressInput)
ValueOutput = grp.getvalue(AddressOutput)
ValueExternalTime = grp.getvalue(AddressExternalTime)
if SetSec == true then
 SetSeconds = 1
 SetSeconds = 60
if ValueExternalTime == nil then
ValueExternalTime = 0
if ValueExternalTime > 0 then
 StairCaseTime = ValueExternalTime * SetSeconds * SetFac
 StairCaseTime = SetDelay * SetSeconds * SetFac
if ValueInput == true then
 --check for earlier started scrips
 --check storage for stpid value
 stpid = storage.get(StaircaseName)
 --check if stpid has a value
 if stpid == nil then
         pid = os.getpid()
         storage.set(StaircaseName, pid)
         -- kill earlier running script
         os.kill(stpid, signal.SIGKILL)
       -- create new pid for next time to kill
         pid = os.getpid()
 if ValueOutput == false then
   grp.write(AddressOutput, true)
   ValueOutput = true
 -- Check time left indication is used
 if UseTimeLeft == true then
   if StairCaseTime > 0 then
       grp.update(AddressTimeLeft, StairCaseTime)
       repeat
         StairCaseTime = StairCaseTime - 1
         os.sleep(1)
       until StairCaseTime == 0
   os.sleep(StairCaseTime)
 if ValueOutput == true then
       grp.write(AddressInput, false)
     ValueInput = false
   if Off_by_Value_Zero == false then
           grp.write(AddressOutput, false)
       ValueOutput = false
     -- Do nothing, this will trigger else condition below on next run
   grp.update(AddressTimeLeft, 0)
   pid = nil
(16.12.2018, 00:08)Erwin van der Zwart Wrote: Hi,
SetDelay = 10
SetFac = 1
 -- Exit script
 return
 SetSeconds = 1
 SetSeconds = 60
         pid = os.getpid()
         pid = os.getpid()
   ValueOutput = true
       repeat
         os.sleep(1)
     ValueInput = false
       ValueOutput = false
   pid = nil
Thanks alot. Will not be improved by me, because Lua is not my strong side at all. But will definitly test it.. Thanks alot.
I gonna create three virtual objects and then  i am wondering whats the correct datatype. Is it 10 Time/date. ?
I just checked the code and the time left is just a integer in seconds, so a 2 byte int should be used.
Erwin,
sorry, should it be a resident script? If yes wich delay should be used?
Can you pls a little more in detail describe your script data types? Is it correct:
6/0/0 Boolean
6/0/1 Boolean
6/0/2 2 bytes unsigned int
6/0/3 2 bytes unsigned int
I tried to make resident script with 1 sec delay and have error:
Resident script:38: attempt to index global 'event' (a nil value)
stack traceback:
Here is a improved version: (event based on trigger object "32/1/100" of light switch)
-- ** Staircase logic with external time object and retriggering on input object Version 3.2 ** --
AddressOutput = '32/1/101'  -- 01. 1 bit (boolean)
AddressExternalTime = '32/1/102' -- 07. 2 byte unsigned integer
AddressTimeLeft = '32/1/103' -- 10. 3 byte time/day
SetDelay = 300 -- 5 minutes
SetFac = 1
Input_Value = event.getvalue()
if Off_by_Value_Zero == false and (Input_Value == false or Input_Value == 0) then
 return
 tpid = storage.get('PID:' .. _SCRIPTNAME)
 if tpid == nil then
     pid = os.getpid()
     storage.set('PID:' .. _SCRIPTNAME, pid)
   pid = os.getpid()
   os.kill(tpid, signal.SIGKILL)
  function Calculate_Time(StairCaseTime)
    if StairCaseTime > (86400 -1) then
      StairCaseTime = (86400 -1)
    local hours = math.floor(StairCaseTime / 3600 % 24)
    local minutes = math.floor(StairCaseTime / 60 % 60)
    local seconds = math.floor(StairCaseTime % 60)
    time = {
      day = 0,
      hour = hours,
      minute = minutes,
      second = seconds,
    return time
 if Input_Value == true or Input_Value == 1 then
   ValueExternalTime = grp.getvalue(AddressExternalTime) or SetDelay
     Multiply_Seconds = 1
     Multiply_Seconds = 60
   StairCaseTime = ValueExternalTime * Multiply_Seconds * SetFac
       time = Calculate_Time(StairCaseTime)
       grp.update(AddressTimeLeft, time)
       repeat
         os.sleep(1)
 elseif Input_Value == false or Input_Value == 0 then
       time = Calculate_Time(0)
 storage.delete('PID:' .. _SCRIPTNAME)
Use these objects types:
Erwin BIG THANKS Smile
Erwin, any idea why i get 1 hour before my time. The minutes is correct and the output changes after minutes are elapsed.
But the hour says 1 and not 00 like your picture Smile
Hi guys, I have in front hour = 2 Smile Just now started this script for testing...
Erwin, what it could be? (May be time difference? I have eastern Europe time zone (+2 hours), but how it can influence here??) I think error in in time calculation function..
Yes there was a small issue with timezones, i did not take that into account, sorry (:
I updated the sample so use the new one or replace this function in your current script:
   time = {
     day = 0,
     hour = hours,
     minute = minutes,
     second = seconds,
   return time
I see this code potentially dangerous. I think there is small but still chance you hit a different running process with the same PID after LM restart. Isn't there more "clean" solution? Mutexes, semaphores etc?
How about adding new function script.NumActive() which returns number of parallel running instances of the same script? And call this function in the loop cycle after sleep and exit the cycle after the returned value is bigger than 1?
 if tpid == nil then
     pid = os.getpid()
   pid = os.getpid()
Event scripts are not the best approach for timers. Either scheduled for resolution of 1 minute or more, or resident for more precise timers.
Semaphores for event script locking are already present: http://openrb.com/docs/semaphore.htm
Great work as always Erwin.
Any idea why yhe mosaic wont show the value of the 3 byte value. Showed it when i used the 2 byte value in seconds and in minutes.
But when i changed the adress and upgraded the mosaic it wont show the value any longer.
Just tested it with time so definitly now showing 3 byte values.
(20.12.2018, 22:27)Tokatubs Wrote: Great work as always Erwin.
Date/time object is not supported in this widget, convert it to string and use 250byte
OK. Cant seem to find converter for that under the converter in FBEDITOR. Then i maybe need to search for a script to convert the value.
Thanks for input.
Before each
paste this
time =string.format('%02d:%02d:%02d',time.hour,time.min,time.sec)
It will convert time to string so just change this object DPT to 250 string
Hi Daniel,
Change StairCaseTime.hour to time.hour etcetera
And put it in the function just before: return time
(21.12.2018, 12:31)Erwin van der Zwart Wrote: Hi Daniel,
true, thanks updated
AddressOutput = '32/1/21'  -- 01. 1 bit (boolean)
AddressExternalTime = '32/1/22' -- 07. 2 byte unsigned integer
AddressTimeLeft = '32/1/23' -- 10. 3 byte time/day
SetSec = false -- Set to false for Minutes
SetFac = 1
 return
 if tpid == nil then
     pid = os.getpid()
   pid = os.getpid()
   time = {
     day = 0,
     hour = hours,
     minute = minutes,
     second = seconds,
   return time
       repeat
         os.sleep(1)
Is this somewhat correct then? Not getting anything on the remaining time block..
I think above just copy of previous post...
Guys, can you please post here final script?? I tried to make changes mentioned but not work for me..