Threads: 57
Hi.
If i tag 20 Objects with the same text, will an event script marked with that tag run 20 times?
Kai-Roger
No, it will run once. Tags allow mapping one script to more than one group address. You can the use event.dst variable contents to perform actions based on current group address.
Threads: 31
(17.12.2018, 08:56)Kai-Roger Wrote: (17.12.2018, 08:41)admin Wrote: No, it will run once. Tags allow mapping one script to more than one group address. You can the use event.dst variable contents to perform actions based on current group address.
What does "event.dst variable contents" mean?
It gives you group address which triggered the script
Threads: 8
21.02.2019, 22:12
(This post was last modified: 21.02.2019, 22:13 by Erwin van der Zwart.)
event.dst returns the address so the correct way to compare is:
if event.dst == '1/1/1' then
—Your action here
grp.find returns all object details in a table so you can’t compare that with event.dst that is returned as a string.
Threads: 8
21.02.2019, 23:07
(This post was last modified: 21.02.2019, 23:09 by Erwin van der Zwart.)
Tip: try to log your variables to see what they hold, Then you know what to do (:
log(event) -> event table including dst
log(event.dst) -> address
log(grp.find(event.dst)) -> table with object details like updatetime, name etc.