Hi.
I am new to this type of programming and had no problem with the block programing they used before but the fb is simply not working for me.
I am trying to controll my light to go on below X LUX and of above Y lux.
I simply doesnt get it to work.
Any ideas?
Thanks!
Threads: 31
Try this
Code: lux = grp.getvalue('1/1/1')
setpoint = grp.getvalue('1/1/2')
output = '1/1/3'
hysteresis = 20 --in %
Limit_ON = setpoint - ((hysteresis/100)*setpoint)
Limit_OFF = setpoint + ((hysteresis/100)*setpoint)
if (lux >= Limit_OFF) then
grp.checkwrite(output, false)
elseif (lux <= Limit_ON) then
grp.checkwrite(output, true)
Threads: 5
Thank you very much for your reply!
Unfortunately I dont get it to work.
created a resident script with the code and changed the adresses but doesnt look like the output changes regarldess of lux or input.
I am probably doing something wrong but I dont know what.
Threads: 31
Yes there was stupid mistake in line 3 corrected the original script
Threads: 5
(22.12.2018, 18:36)Daniel. Wrote: Yes there was stupid mistake in line 3 corrected the original script
Works perfectly! Thank you so much!!!
Threads: 15
(22.12.2018, 17:54)Daniel Wrote: Try this
output = '1/1/3'
I would like to replace the hysteresis from this script for a time period. So let's say i want an hysteresis for 30 minutes how can this be done?
You can use grp.find() and updatetime field to check when the last telegram was sent to this specific object. Then use os.time() to calculate the delta.
Alternative solution is to use a scheduled script that runs every X minutes.
Threads: 15
(14.03.2024, 09:26)admin Wrote: You can use grp.find() and updatetime field to check when the last telegram was sent to this specific object. Then use os.time() to calculate the delta.
Hi admin that will not work for me as the updatetime of the object is changing all the time.
Code: lux = grp.getvalue('1/0/3')
azimut = grp.getvalue('5/5/2')
alarm = grp.getvalue('4/0/1')
hysterese = 10
if alarm == false then
if lux > 700 then
if azimut > 95 and azimut < 150 then
grp.write('2/3/1', 100)
grp.write('2/3/2', 0)
grp.write('2/3/6', 0)
elseif azimut > 180 and azimut < 230 then
grp.write('2/3/1', 0)
grp.write('2/3/2', 100)
elseif azimut > 230 and azimut < 280 then
grp.write('2/3/6', 100)
elseif lux < 500 then
object = grp.find('1/0/3')
time = object.updatetime -- time will change every time the object is updated
Either use storage to save the time when the script was run previously. Or use a scheduled script instead of event.
Threads: 15
(14.03.2024, 09:49)admin Wrote: Either use storage to save the time when the script was run previously. Or use a scheduled script instead of event.
ok clear thanks.
Threads: 19
Hello Admin,
I have a project where I want to use the script below to do a simple light control in steps. Can you please help me to achieve the same functionality but for multiple lights groups.
This will be a resident script with sleep time 10sec. I was thinking if I can create a table to map all variables and then a function to execute every 10sec. Or any better idea
Code: ------Global Settings---------
min = 10
max = 100
hysteresis = 20
--------Light Group 1---------
local current = grp.getvalue('3/0/11') --Area Lux Value
local setpoint = grp.getvalue('3/1/11') --Area Lux Setpoint Value
local output = '3/3/11' --Dim output
local active = grp.getvalue('0/0/211') --Light Control is active or not
local disv = grp.getvalue('2/4/11') --Status dim value
local deltasc = setpoint - current
local deadband = math.abs(deltasc) < hysteresis
local diva_up = disv + 5
local diva_down = disv - 5
local diva_up = math.min(diva_up, max)
local diva_down = math.max(diva_down, min)
if active and not deadband then
if disv ~= 0 then
if current < setpoint then
grp.checkwrite(output, diva_up)
elseif current > setpoint then
grp.checkwrite(output, diva_down)
--------Light Group 2----------
local current = grp.getvalue('3/0/12')
local setpoint = grp.getvalue('3/1/12')
local output = '3/3/12'
local active = grp.getvalue('0/0/212')
local disv = grp.getvalue('2/4/12')
if disv ~= 0 then
Thank you in advance.
Try this (untested):
Code: min = 10
max = 100
hysteresis = 20
delay = 0.1
lights = {
{ active = '0/0/211', current = '3/0/11', setpoint = '3/1/11', status = '2/4/11', output = '3/3/11' },
{ active = '0/0/212', current = '3/0/12', setpoint = '3/1/12', status = '2/4/12', output = '3/3/12' },
function lightcontrol(opts)
if not grp.getvalue(opts.active) then
return
local current = grp.getvalue(opts.current) -- Area Lux Value
local setpoint = grp.getvalue(opts.setpoint) -- Area Lux Setpoint Value
if math.abs(current - setpoint) < hysteresis then
return
local status = grp.getvalue(opts.status) -- Status dim value
if status == 0 then
return
local diva_up = math.min(status + 5, max)
local diva_down = math.max(status - 5, min)
for _, light in ipairs(lights) do
lightcontrol(light)
os.sleep(delay)