Multi OR port
Hallo,
I need create a OR port with about 90-100 input. I tagged each input in objects window. It's possible create the OR gate useing the tag of the group address?
I wrote the follow example that don't function:
if (true == grp.tag('LuciScalaA')) then
  grp.write('12/1/21', true)
  os.sleep(100)
  grp.write('12/1/21', false)
See attached
Best regards
grp.tag will always return a table with objects so this is never true or false..
Here are the needed scripts for logical and/or by TAG:
-- Logical OR port by tagged objects
tagname = 'OR_LOGIC'
output = '1/1/1'
for i, object in ipairs(grp.tag(tagname)) do
  if object.data then
    grp.checkwrite(output, true, 1)
    return
grp.checkwrite(output, false, 1)
-- Logical AND port by tagged objects
tagname = 'AND_LOGIC'
output = '1/1/1'
 if not object.data then
   return
Here is universal script
https://forum.logicmachine.net/showthrea...18#pid1518
What script is more effective and takes less time and less resources to execute? Something like this:
Quote:value = grp.getvalue('1address')
value2 = grp.getvalue('2address)
value3 = grp.getvalue('3address')
output = 'outputaddress'
if(value or value2 or value3 == true) then
  grp.write(output, true)
  grp.write(output, false)
 Or this one:
Quote:tagname = 'OR_LOGIC'
output = 'output_address'
if object.data then
return
I have many lights and many rooms and if I turn on ALL lights at the same time there are a lot of scripts executing at once, so I need the most perfomance-effective solution.
The best for performance is this
Well you see I have a problem with this one. As I have A LOT lights, it feels that if many lights are turning on/off the script starts to "hang" and doesn't update any addresses any more and then it needs to be disabled/enabled to work again. I've tried upgrading LM to newest version but it didn't help so I'm kind of stuck with those 2 scripts.
If you have a lot of lights then this script is much better as it is just one PID, The other creates a lots of them with each telegram sent. Can you send me your project to PM to check why it is happening, It could be some bug or other reason.
Are you using a os.sleep in your script?
If you do that in a event script you might have several scripts running in paralel..