modbus register floating points
I am reading 16 energy meters "ELNET PowerMeters" with spacelynk and my problem is that when reading a record I always read whole values, for example 230 V or 105 A. And I need to read values with floating point.
According to the map of records, I have to read 2 variables and I still can not find it.
for example, for line 1 current I am reading record 4013
This is the manufacturer's registration map, where it indicates how to do it on pages 3/77 and 4/77
https://www.ditrade.md/ctrl/Home/Elnet/E...t_comm.pdf
I think I should do some script to put together 2 records and get a result and write it in a new group address.
I attach the profile that you create
Your help please
Greetings.
You forgot to attach the profile. Anyway, you don't need additional scripts to read floating point values, just correct profile entries.
(07.03.2019, 18:47)administración Wrote: Has olvidado adjuntar el perfil. De todos modos, no necesita scripts adicionales para leer valores de punto flotante, solo corrija las entradas de perfil.
attached profile
"fabricante": "Elnet",
"description": "ElNet Power Meter",
"cartografía":[
{"bus_datatype": 14, "address": 1, "value_nan": [65472,0], "type": "register", "units": "V", "name": "Voltage linea 1", " tipo de datos ":" uint16 "},
{"bus_datatype": 14, "address": 3, "value_nan": [65472,0], "type": "register", "units": "V", "name": "Voltage linea 2", " tipo de datos ":" uint16 "},
{"bus_datatype": 14, "address": 5, "value_nan": [65472,0], "type": "register", "units": "V", "name": "Voltage linea 3", " tipo de datos ":" uint16 "},
{"bus_datatype": 14, "address": 7, "value_nan": [65472,0], "type": "register", "units": "V", "name": "Voltage linea 1-2" , "tipo de datos": "uint16"},
{"bus_datatype": 14, "address": 9, "value_nan": [65472,0], "type": "register", "units": "V", "name": "Voltage linea 2-3" , "tipo de datos": "uint16"},
{"bus_datatype": 14, "address": 11, "value_nan": [65472,0], "type": "register", "units": "V", "name": "Voltage linea 3-1" , "tipo de datos": "uint16"},
{"bus_datatype": 14, "address": 13, "value_nan": [65472,0], "type": "register", "units": "A", "name": "Current linea 1", " tipo de datos ":" uint16 "},
{"bus_datatype": 14, "address": 15, "value_nan": [65472,0], "type": "register", "units": "A", "name": "Current linea 2", " tipo de datos ":" uint16 "},
{"bus_datatype": 14, "address": 17, "value_nan": [65472,0], "type": "register", "units": "A", "name": "Current linea 3", " tipo de datos ":" uint16 "},
{"bus_datatype": 14, "address": 25, "value_nan": [65472,0], "type": "register", "units": "W", "name": "Potencia Activa", "datatype ":" uint16 "},
{"bus_datatype": 14, "address": 33, "value_nan": [65472,0], "type": "register", "units": "VA", "name": "Potencia Aparente", "datatype ":" uint16 "},
{"bus_datatype": 14, "address": 41, "value_nan": [65472,0], "type": "register", "units": "VAR", "name": "Potencia Reactiva", "datatype ":" uint16 "},
{"bus_datatype": 14, "address": 49, "value_nan": [65472,0], "type": "register", "units": "", "name": "Factor de Potencia", "datatype ":" uint16 "},
{"bus_datatype": 14, "address": 51, "value_nan": [65472,0], "type": "register", "units": "Hz", "name": "Frequency", "datatype" : "uint16"}
.json   ElNet LTE Power Meter.json (Size: 1.89 KB / Downloads: 3)
First, you should find out correct address and byte/word order. You can do this via RTU read test in Modbus tab. Use function #4 (Input register), set address to 0 (if this does not work, try 1). Then try all read swap options until you get a valid reading.