This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm whether you accept or reject these cookies being set.

DALI PROBLEM
#41
(11.12.2020, 10:08)Daniel. Wrote: If you still have the tx error then it is most likely broken interface.
Just to clarify, the partial scan is a scan which will find only devices which have no short address. If a ballast was already used elsewhere and programmed partial scan will not find it.  DALI app for canX dali has more options for this.

Yes, I understand the partial scan, but doing a full search already assigns the short addresses to the ballasts again.

I'll do the test by substituting the LM for the one on the way.

The CANx gateways are much better, it even gives us states and it is a great work that saves. If I could replace the Logic M. with a CANX one and not have to look for the ballasts again it would be great, but this I understand that it cannot be done.
Reply
#42
This LM internal interface can use canX dali app but only this one LM
https://openrb.com/logicmachine5-knx-canx-dali
Reply
#43
Hello, I have finally been able to do the search with a new LM and now the search works.

What can I do with my faulty equipment? I'm going to test it in my test shop and reset it to factory settings in the hope of getting it back.

By the way, I am trying to regulate a Mean Well ballast and it is not possible to lower it from 63%. Is it a ballast problem or is it LM?
Reply
#44
Check minimum dimming value, it is parameter of the ballast, If you can change it lower then you will be able to go lower.
Reply
#45
This is probably a hardware issue that factory reset won't solve. You can send your device to us for repairs.
Reply
#46
(15.12.2020, 15:42)Daniel. Wrote: Check minimum dimming value, it is parameter of the ballast, If you can change it lower then you will be able to go lower.
Hello Daniel, I understand that this parameter is not generated from LM, it is something internal to the ballast. or am I wrong? I have a Mean Well ELG-240H-24B, with the naked eye I can't do anything to it.
Reply
#47
There are two minimums - physical and user-defined. User-defined cannot be lower than physical. You can use querymin/queryphysicalmin to get both minimum values. CANx-DALI has this visible/configurable through UI.
Reply
#48
(16.12.2020, 07:58)admin Wrote: There are two minimums - physical and user-defined. User-defined cannot be lower than physical. You can use querymin/queryphysicalmin to get both minimum values. CANx-DALI has this visible/configurable through UI.

Hi Admin,

in the CAN X gateway I can see that minimum physical value that is equal to 161, but it does not let me download it from there. My led barely dims. If I want to take it to a value lower than 10%, what should I do?
Reply
#49
This means that the ballast cannot produce a value lower than 161. Nothing you can do apart from using a different ballast.
Reply