how to charge fluorescent sign
Hi I will turn on the light every 3 hours for 15 minutes to charge some fluorescent signs between 07-16 when the room is not in use, but stop this feature shown the room is in use. has a motion detector that records whether the room is being used. How to create this code?
I can not use the slave input of the motion detector because the rom starts heating and ventilation.
You can create a scheduled script that runs on a specified time. If room is not occupied then you turn the light on/off:
1/1/1 is occupancy status, 1/1/2 is light output.
Scheduled script parameters:
Minute: 0 for turn on, 15 for turn off
Hour: 7,10,13,16
Day of the month: *
Month of the year: All
Day of the week: All
Turn on:
if not grp.getvalue('1/1/1') then   grp.write('1/1/2', true) end
Turn off:
if not grp.getvalue('1/1/1') then   grp.write('1/1/2', false) end
(03.09.2019, 08:54)admin Wrote: You can create a scheduled script that runs on a specified time. If room is not occupied then you turn the light on/off:
Hour: 7,10,13,16
Day of the month: *
Turn on:
Turn off:
tnx this will work, but is it possible to check more rooms in the same code? how will that code look like?
Create a User library called rooms. Modify rooms table as needed. You can add any number of rows.
rooms = {   { status = '1/1/1', output = '1/1/2' },   { status = '2/1/1', output = '2/1/2' },   { status = '3/1/1', output = '3/1/2' },   { status = '4/1/1', output = '4/1/2' },   { status = '5/1/1', output = '5/1/2' },   { status = '6/1/1', output = '6/1/2' }, } function setrooms(value)   for _, room in ipairs(rooms) do     local status = grp.getvalue(room.status)     if not status then       grp.write(room.output, value)       os.sleep(0.2)     end   end end
Turn on:
require('user.rooms') setrooms(true)
Turn off:
require('user.rooms') setrooms(false)
(05.09.2019, 06:26)admin Wrote: Create a User library called rooms. Modify rooms table as needed. You can add any number of rows.
Turn on:
Turn off:
tnx Smile
