10.11.2019, 08:06
Yes, I've did reboot and all works fine now.
Does reboot is also one of a step in upgrade process?
Please test such things:
- if after upgrading device with event-based tag scripts they are in idle state,
- or what is the state of resident scripts after reboot?
I had such situation that GA appeared on the bus but probably event-based script not react on a tag becaue probably it was in some idle state. When I've saved, disabled, enabled this script and once again send that command to the bus then resident script logged that it received command.
In this idle state it was not important if the ga appeared from bus, from other device or from Object tab. Both not worked.
Does reboot is also one of a step in upgrade process?
Please test such things:
- if after upgrading device with event-based tag scripts they are in idle state,
- or what is the state of resident scripts after reboot?
I had such situation that GA appeared on the bus but probably event-based script not react on a tag becaue probably it was in some idle state. When I've saved, disabled, enabled this script and once again send that command to the bus then resident script logged that it received command.
In this idle state it was not important if the ga appeared from bus, from other device or from Object tab. Both not worked.