Writing setpoint 8bytes
I want to write all the heating and cooling setpoints via BACnet or KNXip. Anyone that has handled this before?
See attachment for comments in the documentation.
Can this be done directly via BACnet or KNXip? Or would I have to script this for each room?
All help on the matter is much appreciated.
Here's how to combined 4 separate object values into a single object:
addrs = { '1/1/1', '1/1/2', '1/1/3', '1/1/4' }
value = ''
for _, addr in ipairs(addrs) do
  val = grp.getvalue(addr)
  enc = busdatatype.encode(val, dt.float16)
  value = value .. enc.dataraw
grp.write('1/1/5', value, dt.raw)
This will work over KNX/IP but not over BACnet. Each BACnet datapoint can only store a single value.