Threads: 24
I have a number of schedules which run scripts to open / close blinds at various times of the day. The same scripts can be run ad-hoc by adjusting sliders on a visualisation.
Is there a way to deactivate / activate a group of schedules from a script - ie: to temporarily stop the automated opening / closing of the blinds.
I contemplated calling script.disable() however I need the scripts to remain enabled at all times to support ad-hoc adjustments of the blinds.
Kind Regards
James
Threads: 35
Schedulers have option to disable/enable by object.
Threads: 24
Hi Daniel
Where do I specify the object to disable / enable a particular schedule?
I can't seem to find this only the option to run / not run on holidays. This would work too if I could dynamically / remove holidays with a script.
Kind Regards
James
Threads: 35
Here
Threads: 24
Hmm ... I don't have that option. For this project we're working with the Clipsal / Schneider 5500SHAC which seems to have an older version of the firmware without this.
Kind Regards
James
Threads: 24
Hi Erwin
I'm not sure I understand.
I gather 'blocking 'is the object which the user would toggle on / off with a button on a visaalisation (to enable / disable a scheduler task)
And 'output' is my scheduler object - which in my case controls the position of the blind.
Where does the if statement go?
Kind Regards
James
Threads: 35
Output of your scheduler goes let say to 0/250/0 and it triggers Erwin's script. Output is the group which goes to your script. The blocking group can be added to visu and if it is false then schedule events will be sent if it is true then schedule events will be blocked.
Threads: 24
Ahhh .. I understand!
Thanks you both for explaining.
Kind Regards
James
Threads: 35
This works only one way.