This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

the average value of tagged objects
#14
HI, 
I've tried this script also for obtaining an average value of some temperature values obtained from a temperature sensor that send values at 5-10 second.
The script should work at each 10 min(scheduled script), and calculate the average value for the elapsed time from the last run
Maybe something I make wrong, or I just miss something.

13/2/9 - is the GA where the sensor sends the values
13/2/11 - should be the average value of received value.

This is script:
Code:
if not client then
 -- each group has 3 fields:
 -- tag - status object tag
 -- output - status output object
 -- mode - calculate mode (and/or/avg)
 groups = {
 
   { tag = '13/2/9', output = '13/2/11', mode = 'avg' },
 }

 -- time to wait between last telegram from any status in group and update
 updatedelay = 0.5

 -- object value cache
 values = {}

 -- object datatype cache
 datatypes = {}

 -- send update only when value changes
 grp.checkupdate = function(alias, value)
   if values[ alias ] ~= value then
     grp.update(alias, value)
   end
 end

 calc = {}

 -- AVERAGE value
 calc['avg'] = function(group)
   local result, count, value = 0, 0

   for _, address in ipairs(group.objects) do
     value = values[ address ]

     -- number must be in [0..100] range
     if type(value) == 'number' then
       result = result + value
       count = count + 1
     -- boolean true is 100%, false is 0%
     elseif type(value) == 'boolean' then
       if toboolean(value) then
         result = result + 100
       end

       count = count + 1
     end
   end

   if count > 0 then
     result = math.floor(result / count + 0.5)
     grp.checkupdate(group.output, result)
   end
 end

 -- AND gate
 calc['and'] = function(group)
   local result = true

   for _, address in ipairs(group.objects) do
     result = result and toboolean(values[ address ])
   end

   grp.checkupdate(group.output, result)
 end

 -- OR gate
 calc['or'] = function(group)
   local result = false

   for _, address in ipairs(group.objects) do
     result = result or toboolean(values[ address ])
   end

   grp.checkupdate(group.output, result)
 end

 -- prepare each group
 for _, group in ipairs(groups) do
   object = grp.find(group.output)

   -- cache output status object value and datatype
   values[ object.address ] = object.data
   datatypes[ object.address ] = object.datatype
   group.output = object.address

   -- group input status object list
   group.objects = {}

   -- find all status objects and cache values and datatypes
   objects = grp.tag(group.tag)
   for _, object in ipairs(objects) do
     values[ object.address ] = object.data
     datatypes[ object.address ] = object.datatype
     table.insert(group.objects, object.address)
   end

   -- force update on first run
   group.timer = 0

   -- calc function reference
   group.fn = calc[ group.mode ]
 end

 -- handle group writes
 function eventhandler(event)
   local dst, datatype

   dst = event.dst
   datatype = datatypes[ event.dst ]
   -- unknown object, stop
   if not datatype then
     return
   end

   values[ dst ] = dpt.decode(event.datahex, datatype)

   -- check if any group needs to be updated
   for _, group in ipairs(groups) do
     for _, address in ipairs(group.objects) do
       if address == dst then
         group.timer = updatedelay
       end
     end
   end
 end

 require('genohm-scada.eibdgm')
 client = eibdgm:new({ timeout = 0.25 })
 client:sethandler('groupwrite', eventhandler)
end

tsec, tusec = os.microtime()
client:step()
delta = os.udifftime(tsec, tusec)

-- check if any group has an active timer
for _, group in ipairs(groups) do
 timer = group.timer

 if timer then
   timer = timer - delta

   -- timer expired, run calc function
   if timer <= 0 then
     group.fn(group)
     timer = nil
   end

   group.timer = timer
 end
end