250 byte string: strange behavior
require('custom.fbeditor20.Time')
functions_Time_json_fbe_operating_hours_input_1 = grp.find('0/1/1')
functions_Time_json_fbe_operating_hours_input_2 = grp.getvalue('32/1/3')
hours = fbe_operating_hours(functions_Time_json_fbe_operating_hours_input_1, functions_Time_json_fbe_operating_hours_input_2, 'fb__New_diagram__fbe_operating_hours__id')
if hours ~= nil then
    grp.checkupdate('32/1/2', hours, 0.01)
value = grp.getvalue('32/1/2')
x = math.floor(value)
y = value - x
z = math.ceil(y * 60)
grp.write('32/1/4', x .. ":" .. z) -- 32/1/4 address 250 byte string
Hi there, I use math.floor function to make readable in time format the value of timer. Everything works fine (if 32/1/2 is 3,5 then 32/1/4 = 3:30) but when value of 32/1/2 does not change I do not read 3:30 anymore but a strange string ASCII.
How is it possible? It seems it happens only in a LM machine. In another is ok.
What value exactly do you get in 32/1/4? Try adding log(value, x, y, z) before grp.write to check the variable contents.
Also getvalue() there is not needed since hours variable already contains the same value.
  return
hour = math.floor(hours)
minutes = string.format('%02d', math.floor((hours % 1) * 60))
text = hour .. ':' .. minutes
grp.write('32/1/4', text)
(02.12.2020, 09:01)admin Wrote: What value exactly do you get in 32/1/4? Try adding log(value, x, y, z) before grp.write to check the variable contents.
  return
Enclosed what I mean. But the log of hour and minutes is correct. It seems that this problem occurs only in the machine LM5CLp2.
In LM5Lite knx no problem.
Do you have FB editor with same version on both devices?
Is the value displayed correctly in the object list in LM configurator? Or is it the same as in Mosaic?
(02.12.2020, 12:42)admin Wrote: Is the value displayed correctly in the object list in LM configurator? Or is it the same as in Mosaic?
Hi admin,the fb editor is the same. And the problem occurs in Mosaic and object list as well.
Br
Can you provide a backup from this device?
(02.12.2020, 12:53)admin Wrote: Can you provide a backup from this device?
Sent you by private message.
You have a resident script "Date & Time" that's writing different data to the same object:
grp.update('32/1/4', time, dt.time)
I am sorry for that! I did not check inside that script which I do not use.
I have to send you a gift for Xmas.
Thank you mate!!