This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Trends API
#6
Here is a script to create trends as batch from start address until end address for new (and relaese candidate) FW.


Code:
-- Batch adding trends - Created by Erwin van der Zwart - Schneider Electric Netherlands -----------
-- For spaceLYnk FW 1.2.1 or higher and homeLYnk FW 1.5.1 or higher --------------------------------
-- Refresh browser after creation to show the trends -----------------------------------------------
----------------------------------------- Start Parameters -----------------------------------------

-- Start address of objects
start_objectaddress = '1/1/1'

-- Trends for all objects between these range are created

-- End address of objects
end_objectaddress = '1/1/3'

-- Set username and password for access to HL
username = 'admin'
password = 'admin'

-- Select trend type to create (or multiple types on same object)
create_trendtype_counter = true
create_trendtype_counter_with_negative_delta = true
create_trendtype_absolute_value = true

-- Set trend precicion (!Important! Can only be these values: 0 to 8)
trendprecision = 2

-- Set trend resolution (!Important! Can only be these values: 5 / 10 / 15 / 20 / 30 / 60 minutes))
trendresolution = 5

-- Set trend count resolution (!Important! Can only be these values: '30' = 30 days, '180' = 180 days, '365' = 1 year, '730' = 2 years, '1825' = 5 years
trendcountresolution = 365

-- Set trend count days (!Important! Can only be these values: '1' = 1 year / '2' = 2 years / '5' = 5 years / '10' = 10 years)
trendcountdaily = 10

-- Set show always 0 base line
trendshowzero = 0 -- 0 = disabled 1 = enabled

------------------------------------------ End Parameters ------------------------------------------
------------------------------ DON'T CHANGE ANYTHING UNDER THIS LINE -------------------------------
-- Load modules
require('json')
require('socket.url')
require('socket.http')

-- Set HL ip address as localhost
ip = '127.0.0.1'

-- Calculate start address to DB format
start_objectaddress = knxlib.encodega(start_objectaddress)

-- Calculate end address to DB format
end_objectaddress = knxlib.encodega(end_objectaddress)

-- Create url for trend creation
url = 'http://' .. username .. ':' .. password .. '@' .. ip .. '/scada-main/trends/save'

-- Function to send request to create trend
function url_send(trend_object, trend_name, trend_type, trend_resolution, trend_precision, trend_count_resolution, trend_count_daily, trend_show_zero, trend_id)
 local trend = {
     object = trend_object,
     name = trend_name,
     type = trend_type,
     resolution = trend_resolution,
     precision = trend_precision,
   count_resolution = trend_count_resolution * 12 * 24, -- nr of days * nr of points in a hour at min resolution (60/5 = 12) * hours per day
   count_daily = trend_count_daily * 365, -- nr of days * 365 days a year
     show_zero = trend_show_zero,
     id = trend_id,
    }
 data = json.encode(trend)
    form_data = 'data=' .. socket.url.escape(data)
    socket.http.TIMEOUT = 15  
    local res, code, response_header = socket.http.request(url, form_data)
 return res, code, response_header
end

-- Set counters for creation log
number_of_trends = 0
number_failed = 0

-- Loop from startadres to end address to create trends
for i = start_objectaddress, end_objectaddress, 1 do
 
 -- Get current group address from loop
 current_GA = knxlib.decodega(i)
 
 -- Get current object info
 objectinfo = grp.find(current_GA)
    
 -- Check if object excists
 if objectinfo ~= nil then
     
   -- Set parameters for request
   trendobject = objectinfo.id
   trendname = objectinfo.name
   trendid = ''
   
   -- Check if trend type 'Counter' should be created
   if create_trendtype_counter == true then
     
     -- Call function to send create request
     result, code, response_header = url_send(trendobject, trendname, 'C', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
     
     -- Calculate results for creation results log
       if result == '{"success":true}' then
         number_of_trends = number_of_trends + 1
       else
         number_failed = number_failed + 1
       end
     
   end
   
   -- Check if trend type 'Counter with negative delta' should be created
   if create_trendtype_counter_with_negative_delta == true then
     
            -- Call function to send create request
     result, code, response_header = url_send(trendobject, trendname, 'D', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
         
     -- Calculate results for creation results log
       if result == '{"success":true}' then
         number_of_trends = number_of_trends + 1
       else
         number_failed = number_failed + 1
       end
     
   end
   
   -- Check if trend type 'Absolute value' should be created
   if create_trendtype_absolute_value == true then
            
     -- Call function to send create request
     result, code, response_header = url_send(trendobject, trendname, 'G', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
         
     -- Calculate results for creation results log
       if result == '{"success":true}' then
         number_of_trends = number_of_trends + 1
       else
         number_failed = number_failed + 1
       end
     
   end
   
 end
 
end
   
if number_failed == 0 then
    log ("Created " .. number_of_trends .. " trends succesfully")
else
    log ("Created " .. number_of_trends .. " trends succesfully and creation of " .. number_failed .. " trends failed")
end

-- Disable script when done automaticly
script.disable(_SCRIPTNAME)


Here is a script to batch export last month trend data as csv and send by mail (with trend selection) for new (and relaese candidate) FW.

Code:
--**************************************************************************--
--** Email trendlog data as CSV attachment created by Erwin van der Zwart **--
--************ For HL from FW 1.5 and SL from FW 1.2 with NGINX ************--
--**************************************************************************--
--*************************** Start of parameters **************************--
-- Version 1.1 *************************************************************--

--Gmail (smtp) username !IMPORTANT!
user = 'YOUR EMAIL ADRESS'

--Gmail (smtp) password !IMPORTANT!
password = 'YOUR PASSWORD'

--Sender for e-mail
from = '<' .. user .. '>'
alias_from = 'YOUR ALIAS'

--Recipient for e-mail
to = '<receiver@domain.com>'
alias_to = 'receiver'

--Subject for e-mail
subjectpart1 = 'Trend export file'
subjectpart2 = 'automaticly send by homeLYnk'

--Message on bottom of email (will only be showed when client don't understand attachment)
epilogue = 'End of message'

--Set export mode (selected trend(s) or all trends)
export_all = true

--Set trend names if not all trends need to be exported (only used when export_all = false)
trendnames = {
 "Total Electric Usage",
 "Total Water Usage",
 "Total Gas Usage",
}

--**************************************************************************--
--**************************** End of parameters ***************************--
--**************************************************************************--
--****************** DON'T CHANGE ANYTHING UNDER THIS LINE *****************--
--**************************************************************************--

require('trends')

-- Get all trend names from DB
trends_table = db:getall('SELECT name FROM trends ORDER BY name DESC')

-- Check if all trends or selection neeed to be exported
if export_all == false then
 -- Loop through trends_table
 i = 1
for _, trend_names in ipairs(trends_table) do
   delete_from_table = true
   -- Loop through trendnames
   for _, trendname in ipairs(trendnames) do
     if trendname == trend_names.name then
   delete_from_table = false
     end
   end
   if delete_from_table == true then
     table.remove(trends_table, i)
 end
 i = i + 1
 end
end

-- Check if the is at least 1 trend to be exported
if #trends_table < 1 then
 log("No trends available, Could not export trends")
 return
end

-- csv buffer
buffer = {}

-- Add to buffer
table.insert(buffer, '"This file contains the export data of ' .. #trends_table .. ' trend(s) and is automaticly created on ' .. os.date("%A",os.time()) .. ' ' .. os.date("%d-%m-%y at %H:%M") .. '"')
-- Add empty line
table.insert(buffer, '""')

-- months
local months = { "Januari", "Februari", "March", "April", "May", "June", "July", "August", "September", "October", "November", "December" }

-- Loop through trends_table
for _, trend_names in ipairs(trends_table) do
 -- Grab trend name from DB table
 trend_name = trend_names.name
 
 -- Add to buffer
 table.insert(buffer, '"##### START OF TREND ' .. _ .. ': ' .. trend_name .. ' #####"')
 -- Add empty line
 table.insert(buffer, '""')

-- Get current timestamp
 timestamp = os.time()
startpoint = os.date('*t', timestamp)
endpoint = os.date('*t')

-- Reset to first of month
startpoint.sec = 0
startpoint.min = 0
startpoint.hour = 0
startpoint.yday = startpoint.yday - (startpoint.day -1)
startpoint.day = 1
startpoint.wday = 1

endpoint.sec = 0
endpoint.min = 0
endpoint.hour = 0
endpoint.yday = endpoint.yday - (endpoint.day -1)
endpoint.day = 1
endpoint.wday = 1

-- Get data for the past month
dates = {}
 dates['start'] = startpoint
 
 if dates['start'].month == 1 then
 dates['start'].month = 12
   dates['start'].year = dates['start'].year - 1
 else
   dates['start'].month = dates['start'].month - 1
 end
 
 dates['end'] = endpoint
 dates['end'].month = dates['start'].month + 1
 
 -- Set resolution to dayly data
 resolution = 86400
 
 -- Get last month for data by each days in this month
 trenddatamonth = trends.fetch(trend_name, dates, resolution)
 
 -- Get last month total avarage data
 trenddatamonthavg = trends.fetchone(trend_name, dates, resolution)
 
 -- Add to buffer
 table.insert(buffer, '"Export of the average usage of the month ' .. months[dates['start'].month] .. ' from trend ' .. trend_name .. '"')
 -- Add empty line
 table.insert(buffer, '""')
 -- Add header
 table.insert(buffer, '"Start date","End Date","Average month value"')
 -- Add to buffer
 table.insert(buffer, '"01-' .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year .. '","' .. #trenddatamonth .. '-' .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year .. '","' .. trenddatamonthavg .. '"')
 -- Add empty line
 table.insert(buffer, '""')
 -- Add to buffer
 table.insert(buffer, '"Detailed export of the daily usage of the month ' .. months[dates['start'].month] .. ' from trend ' .. trend_name .. '"')
 -- Add empty line
 table.insert(buffer, '""')
 -- Add header
 table.insert(buffer, '"Weekday","Date","Average day value"')
 for _, row in ipairs(trenddatamonth) do
   stamp = dates['start'].year .. '-' .. dates['start'].month .. '-' .. string.format("%02d", _)
local y, m, d = stamp:match("(%d+)%-(%d+)%-(%d+)")
local t = { year = y, month = m, day = d}  
   -- format csv row
   csv = string.format('%q,%q,%q', os.date("%A",os.time(t)), "" .. string.format("%02d", _) .. "-" .. string.format("%02d", dates['start'].month) .. "-" .. dates['start'].year, row)
   -- add to buffer
   table.insert(buffer, csv)
 end
 -- Add empty line
 table.insert(buffer, '""')
 -- Add header
 table.insert(buffer, '"##### END OF TREND ' .. _ .. ': ' .. trend_name .. ' #####"')
 -- Add empty line
 table.insert(buffer, '""')
end

--Create table to include mail settings
local settings = {
   from = from,
   rcpt = to,
   user = user,
   password = password,
   server = 'smtp.gmail.com',
   port = 465,
   secure = 'sslv23',
}

--Create attachment inside FTP server
src = 'Trend Export '.. os.date('%Y-%m-%d %H#%M#%S') .. '.csv'
dst = '/home/ftp/' .. src
io.writefile(dst, buffer)

--Create subject
subject = subjectpart1 .. ": " .. src .. " " .. subjectpart2

--Load required modules to send email with attachment
local smtp = require("socket.smtp")
local mime = require("mime")
local ltn12 = require("ltn12")

--Create e-mail header
settings.source = smtp.message{
headers = {
         from = '' .. alias_from .. ' ' .. from .. '',
         to = '' .. alias_to .. ' ' .. to .. '',
         subject = subject
},

--Load attachment inside body    
body = {
preamble = "",
[1] = {  
       headers = {
          ["content-type"] = 'text/plain',
          ["content-disposition"] = 'attachment; filename="'..src..'"',
          ["content-description"] = '.. src ..',
          ["content-transfer-encoding"] = "BASE64",
       },
       body = ltn12.source.chain(
         ltn12.source.file(io.open(dst, "rb")),
         ltn12.filter.chain(
         mime.encode("base64"),
         mime.wrap()
       )
     )
   },
     epilogue = epilogue
 }
}

--Send the email
r, e = smtp.send(settings)

--Create alert when sending gives an error with error message
if (e) then
 log (e)
 log (r)
 alert("Could not send email: ", e, "\n")
end

--Delete created temp csv file from ftp folder inside HL
os.remove(dst)

BR,

Erwin van der Zwart
Reply


Messages In This Thread
Trends API - by buuuudzik - 28.05.2016, 16:52
RE: Trends API - by Habib - 28.05.2016, 17:13
RE: Trends API - by Erwin van der Zwart - 28.05.2016, 22:01
RE: Trends API - by admin - 29.05.2016, 06:12
RE: Trends API - by buuuudzik - 29.05.2016, 11:22
RE: Trends API - by Erwin van der Zwart - 02.09.2016, 18:46
RE: Trends API - by admin - 05.09.2016, 06:01
RE: Trends API - by Erwin van der Zwart - 05.09.2016, 09:29
RE: Trends API - by Pawel - 07.12.2016, 20:15
RE: Trends API - by Domoticatorino - 19.02.2018, 15:39
RE: Trends API - by Erwin van der Zwart - 19.02.2018, 16:32
RE: Trends API - by Domoticatorino - 13.02.2018, 16:52
RE: Trends API - by Daniel - 13.02.2018, 18:49
RE: Trends API - by Domoticatorino - 19.02.2018, 16:33
RE: Trends API - by PassivPluss - 17.09.2019, 21:10
RE: Trends API - by admin - 24.09.2019, 06:53
RE: Trends API - by Trond Hoyem - 17.06.2022, 12:57
RE: Trends API - by admin - 17.06.2022, 13:20
RE: Trends API - by Trond Hoyem - 17.06.2022, 13:23
RE: Trends API - by admin - 17.06.2022, 13:23
RE: Trends API - by Trond Hoyem - 17.06.2022, 13:27
RE: Trends API - by admin - 17.06.2022, 13:30
RE: Trends API - by Trond Hoyem - 17.06.2022, 13:33
RE: Trends API - by admin - 17.06.2022, 13:34
RE: Trends API - by Trond Hoyem - 17.06.2022, 13:36
RE: Trends API - by admin - 17.06.2022, 14:15
RE: Trends API - by Trond Hoyem - 17.06.2022, 14:26
RE: Trends API - by admin - 17.06.2022, 14:32

Forum Jump: