This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

PID Problem
#5
Since the output is not connected your test won't show any real data because PID requires feedback from the system to operate. As I've mentioned start with a single PID controller with all 3 gains set to 1. You have to see how it operates in real conditions before applying any tuning. Trend log will help you to see how high the system oscillations are.
Reply


Messages In This Thread
PID Problem - by MantasJ - 13.02.2021, 14:56
RE: PID Problem - by MantasJ - 13.02.2021, 16:11
RE: PID Problem - by admin - 15.02.2021, 10:30
RE: PID Problem - by MantasJ - 15.02.2021, 12:07
RE: PID Problem - by admin - 15.02.2021, 12:25
RE: PID Problem - by MantasJ - 15.02.2021, 12:41
RE: PID Problem - by admin - 15.02.2021, 14:06