Counter and Trend
I am unsure how to realize this: I have a reed contact attached to the re:actor. I want to count the times it gets opened and log this, but I also would like to use it in a trend to see how often the reed gets opened in a day,week,month.
Cheers!
You can create an event script which increases object value on each run. Trend will automatically show how many events happened during selected period. You can also get trend data from Lua to display certain stats: http://openrb.com/docs/
value = grp.getvalue('1/1/1') grp.update('1/1/1', value + 1)
(06.06.2016, 13:19)admin Wrote: You can create an event script which increases object value on each run. Trend will automatically show how many events happened during selected period. You can also get trend data from Lua to display certain stats: http://openrb.com/docs/
Tip: Use a 12. 4 byte unsigned integer object to have maximum size to count without exponent and also use:
value_reed = event.getvalue()
if value_reed == true then
     if value >= (256*256*256*256) then -- max of 12. 4 byte unsigned integer object
        grp.update('1/1/1', 0) -- reset object value to zero to start counting from start again
This makes the counting only happening on opening of the reed otherwise the count will happen on opening and closing, and will make the object value jump to 0 when max of object is reached.
Erwin, that check is incorrect
256 * 256 * 256 * 256 = 0x100000000 (4294967296)
Maximum value for unsigned 32-bit integer is 0xFFFFFFFF (4294967295)
if event.getvalue() then   value = grp.getvalue('1/1/1') + 1      -- overflow check   if value > 0xFFFFFFFF then     value = 0   end   grp.update('1/1/1', value) end
(07.06.2016, 06:17)admin Wrote: Erwin, that check is incorrect
Hi Admin,
Yes you are right, i add the +1 after validation, so it will never be that value
Sorry (;