Modbus: can't write on ALDES INSPIRAIR_TOP_B120
I Create the attached modbus profile for the that Aldes module and I can't write on some register like the 257.
I asked their technical support and the answer was:
"There is a particularity on Inspirair to write on a single register.
You need to select a length “2” to write on a single register.
For example to write on address 257 then you need to select register 256 with length 2 and write the value you need on address 257."
So how a have to modify the profile?
Peppe
.json   INSPIRAIR_TOP_B120.json (Size: 1.63 KB / Downloads: 11)
Add "datatype": "uint32"
ok, thank you!