OR LOGIC VIA TAG
could you please check script below. All tagged properly in the project, but when true signal comes from one of 30 objects nothing is being written to group 34/1/10
if not client then
  -- each group has 3 fields:
  -- tag - status object tag
  -- output - status output object
  -- mode - calculate mode (and/or/avg)
  groups =
    { tag = 'ORGATEZONESDEMAND', output = '34/1/10', mode = 'or' }
  -- time to wait between last telegram from any status in group and update
  updatedelay = 0.5
  -- object value cache
  values = {}
  -- object datatype cache
  datatypes = {}
  -- send update only when value changes
  grp.checkupdate = function(alias, value)
    if values[ alias ] ~= value then
      grp.update (alias, value)
  calc = {}
  -- AVERAGE value
  calc['avg'] = function(group)
    local result, count, value = 0, 0
    for _, address in ipairs(group.objects) do
      value = values[ address ]
      -- number must be in [0..100] range
      if type(value) == 'number' then
        result = result + value
        count = count + 1
      -- boolean true is 100%, false is 0%
      elseif type(value) == 'boolean' then
        if toboolean(value) then
          result = result + 100
        count = count + 1
    if count > 0 then
      result = math.floor(result / count + 0.5)
      grp.checkupdate(group.output, result)
  -- AND gate
  calc['and'] = function(group)
    local result = true
      result = result and toboolean(values[ address ])
  -- OR gate
  calc['or'] = function(group)
    local result = false
      result = result or toboolean(values[ address ])
  -- prepare each group
  for _, group in ipairs(groups) do
    object = grp.find(group.output)
    -- cache output status object value and datatype
    values[ object.address ] = object.data
    datatypes[ object.address ] = object.datatype
    group.output = object.address
    -- group input status object list
    group.objects = {}
    -- find all status objects and cache values and datatypes
    objects = grp.tag(group.tag)
    for _, object in ipairs(objects) do
      table.insert(group.objects, object.address)
    -- force update on first run
    group.timer = 0
    -- calc function reference
    group.fn = calc[ group.mode ]
  -- handle group writes
  function eventhandler(event)
    local dst, datatype
    dst = event.dst
    datatype = datatypes[ event.dst ]
    -- unknown object, stop
    if not datatype then
      return
    values[ dst ] = dpt.decode(event.datahex, datatype)
    -- check if any group needs to be updated
        if address == dst then
          group.timer = updatedelay
  require('genohm-scada.eibdgm')
  client = eibdgm:new({ timeout = 0.25 })
  client:sethandler('groupwrite', eventhandler)
tsec, tusec = os.microtime()
client:step()
delta = os.udifftime(tsec, tusec)
-- check if any group has an active timer
  timer = group.timer
  if timer then
    timer = timer - delta
    -- timer expired, run calc function
    if timer <= 0 then
      group.fn(group)
      timer = nil
    group.timer = timer
You are missing {} around groups definition, it should be like this:
groups = {
  { tag = ... }
(26.06.2021, 13:26)admin Wrote: You are missing {} around groups definition, it should be like this:
groups = {
  { tag = ... }
Thank you,
still no update signal coming to 34/1/10. I'm just thinking if in the part --send update  instead of grp.update should be grp.write
grp. write doesn't work either
Works for me (resident, sleep time = 0). Make sure that the output object is created and that it does not have ORGATEZONESDEMAND tag.
if not client then
  groups = {
  updatedelay = 0.5
  values = {}
  datatypes = {}
  calc = {}
  -- AVERAGE value
        count = count + 1
        count = count + 1
    if count > 0 then
  -- AND gate
    local result = true
  -- OR gate
    group.objects = {}
    group.timer = 0
    local dst, datatype
    dst = event.dst
      return
client:step()
  timer = group.timer
  if timer then
    if timer <= 0 then
      group.fn(group)
      timer = nil
    group.timer = timer
