LM5 DW1 4bit with KNX Sensor
Hello everyone
I would like to dim the light using a KNX button (4-bit datapoint).
In the dali tab, i can link this object for the lamp, the dimming works well for one lamp, but as soon as more than 5 lamps with the same data type are controlled, the lamps dim differently and with a delay.
does anyone know a script to control the dali group with 4bit datapoint?
like that:
daligroup=0
if (grp.getvalue('10/0/3') > 1) then
require('user.dali')
dalicmd('internal', 'arc', { addrtype = 'group', address = daligroup, value = (grp.getvalue('10/0/3')*2.54) })
dalicmd('internal', 'arc', { addrtype = 'group', address = daligroup, value = 0 })
thx
used firmware: LM5 Lite+Ext (i.MX6)
produkt: LM5 DW1
There is probably better way but you could convert this script. It was created for short address and to be dimmed bu visu button 4 bit object.
https://forum.logicmachine.net/showthrea...61#pid8061
thank you very much, but this is the wrong way...
I was able to dim with the following script, the problem is that I have to press it every time.
as soon as I press it, it must be sent cyclically, as long as I press the button, it is dimmed (that is normal)
daligroup=0
if (grp.getvalue('10/0/52') == 9) then
dalicmd('internal', 'up', { addrtype = 'group', address = daligroup })
dalicmd('internal2', 'up', { addrtype = 'group', address = daligroup })
elseif (grp.getvalue('10/0/52') == 1) then
dalicmd('internal', 'down', { addrtype = 'group', address = daligroup })
dalicmd('internal2', 'down', { addrtype = 'group', address = daligroup })
big thx
This is why the script I sent you use while loop.
Do as Daniel suggested and use 0.2 seconds sleep time between up/down calls
(10.11.2021, 11:39)Daniel Wrote: There is probably  better way but you could convert this script. It was created for short address and to be dimmed bu visu button 4 bit object.
Hello Daniel
Thank you very much, it worked perfectly
the script controls my dali group with few adjustments