This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

KNX Objects
#3
There is no limit on object creation, you can add the full scope if you like.

But there is a limit in concurrent communication, as with any KNX system you have a limit on the TP, but IP is depending on the CPU load by other stuff you are using, So you can have 10.000 objects that are almost not changing and all works well but you can also have 100 objects changes every 0.1 seconds and your cpu goes through the roof..

So no hard limit, but if you have 4000 objects you really need to think on traffic, are those temperatures and motion telegrams then changes are you have to much traffic for 1 controllers..
Reply


Messages In This Thread
KNX Objects - by CristianAgata - 26.11.2021, 21:38
RE: KNX Objects - by ricole87 - 27.11.2021, 02:20
RE: KNX Objects - by Erwin van der Zwart - 27.11.2021, 08:56
RE: KNX Objects - by ricole87 - 28.11.2021, 13:09