Would it be possible, maybe through websocket? to send heartbeat command to ocpp backend?
What I'm really after is to use a energy meter and send consumption to the backends Load managment but if I could mange to figure out just the heartbeat function I should be able to get the rest working by my self
Is there any solutioon to take information from EV CHARGING Expert SCHNEIDER HMIBSC...
For example take the total/zone consumsion of evlink.... I know we can communicate modbus to the evlink (but I have 20 evlink). I was looking for a solution to interface with the SE EV HMI.
Do you know it ?
thanks
-----------
FRANCE SMARTHOME & SMARTBUILDING INTEGRATION
SE ECO EXPERT
(27.09.2024, 15:26)domotiqa Wrote: Is there any solutioon to take information from EV CHARGING Expert SCHNEIDER HMIBSC...
For example take the total/zone consumsion of evlink.... I know we can communicate modbus to the evlink (but I have 20 evlink). I was looking for a solution to interface with the SE EV HMI.
Do you know it ?
thanks
The EV Charging Expert does not expose that information in the API they developed for the EVCE.
You are better off requesting the info over modbus tcp.
(27.09.2024, 17:13)domotiqa Wrote: ok
I ssaw that we can provide ocpp server on the EV but not yet implemented on LM I guess
I didn't know there was an API
when you say modbus ip you mean to the evlink not the EVCE, cause I didn't find any modbus register for it, only for the evlink station
For the last two years we didn't see any demand from OCPP as all EV chargers did support modbus or other way of communications. Due to this and many versions of the protocol we did freeze any development on this.