Universal Modbus TCP/RTU Slave
A new version of the modbus slave script where you can freely define coil/registers and even use bigger data-types and multiple slaves.
Data-types supported:
  [ dt.bool ] = 1,
  [ dt.bit4 ] = 1,
  [ dt.int8 ] = 1,
  [ dt.uint8 ] = 1,
  [ dt.int16 ] = 1,
  [ dt.uint16 ] = 1,
  [ dt.float16 ] = 1,
  [ dt.int32 ] = 2,
  [ dt.uint32 ] = 2,
  [ dt.float32 ] = 2,
  [ dt.int64 ] = 4,
The number next to DPT is representing how many registers will be used per object. It means if int64 is used make sure to leave gap for 4 registers in the mapping table.
Only 2023 firmware and newer is supported
1. Create user library mbslave and past this code:
local _M = {}
local byteswap, wordswap
local f16mult = 1
local mapping = {}
local exception = {}
local reply = {}
local fncodes = {
  [1] = 'readcoils',
  [2] = 'readdiscreteinputs',
  [3] = 'readregisters',
  [4] = 'readinputregisters',
  [5] = 'writecoil',
  [6] = 'writeregister',
  [15] = 'writecoils',
  [16] = 'writeregisters',
local mapfncodes = {
  [1] = 'coils',
  [2] = 'discreteinputs',
  [3] = 'registers',
  [4] = 'inputregisters',
  [5] = 'coils',
  [6] = 'registers',
  [15] = 'coils',
  [16] = 'registers',
local dtlens = {
  [ dt.bool ] = 1,
  [ dt.bit4 ] = 1,
  [ dt.int8 ] = 1,
  [ dt.uint8 ] = 1,
  [ dt.int16 ] = 1,
  [ dt.uint16 ] = 1,
  [ dt.float16 ] = 1,
  [ dt.int32 ] = 2,
  [ dt.uint32 ] = 2,
  [ dt.float32 ] = 2,
  [ dt.int64 ] = 4,
local maxpdu = 253
local maxaddr = 0x10000
local coilon = 0xFF00
local limits = {
  readbits = 2000,
  writebits = 1968,
  readregisters = 125,
  writeregisters = 123,
local excodes = {
  illegalfunction = 1,
  illegaldataaddress = 2,
  illegaldatavalue = 3,
  serverdevicefailure = 4,
  acknowledge = 5,
  serverdevicebusy = 6,
  negativeacknowledge = 7,
  memoryparityerror = 8,
  gatewaypathunavailable = 10,
  gatewaytargetdevicefailed = 11,
local handlers = {}
local function touint8(buf, off)
  return buf:byte(off)
local function touint16(buf, off, swap)
  local b1, b2 = buf:byte(off, off + 1)
  if swap then
    b1, b2 = b2, b1
  return b1 * 0x100 + b2
local function getmapping(slaveid, fncode)
  local mapfncode = mapfncodes[ fncode ]
  local slave = mapping[ slaveid ]
  if not slave then
    slave = mapping['*']
  if slave then
    return slave[ mapfncode ]
local function readbits(slaveid, fncode, data)
  if #data ~= 4 then
    return
  local addr = touint16(data, 1)
  local count = touint16(data, 3)
  if count == 0 or count > limits.readbits then
    return excodes.illegaldataaddress
  elseif (addr + count) > maxaddr then
  local map = getmapping(slaveid, fncode)
  if not map then
  local res = {}
  local bits, byte = 0, 0
  for i = 0, (count - 1) do
    local mapaddr = map[ addr + i ]
    if mapaddr then
      local bval = grp.getvalue(mapaddr)
      if toboolean(bval) then
        byte = byte + bit.lshift(1, bits)
    bits = bits + 1
    if bits == 8 then
      res[ #res + 1 ] = string.char(byte)
      bits, byte = 0, 0
  if bits ~= 0 then
  return string.char(#res) .. table.concat(res)
local zeroreg = string.char(0, 0)
local function readvalue(res, value, dpt)
  if dpt == dt.float16 then
    value = value * f16mult
    dpt = dt.int16
  local enc = busdatatype.encode(value, dpt)
  if not enc.dataraw then
    return
  local raw = enc.dataraw
  if #raw % 2 == 1 then
    raw = string.char(0) .. raw
  local words = #raw / 2
  local offset = #res
  for i = 1, words do
    local word = raw:sub(i * 2 - 1, i * 2)
    if byteswap then
      word = word:sub(2, 2) .. word:sub(1, 1)
    if wordswap then
      res[ offset + i ] = word
      res[ offset + 1 + words - i ] = word
  return true
local function readregisters(slaveid, fncode, data)
  if #data ~= 4 then
    return
  if count == 0 or count > limits.readregisters then
  if not map then
  local res = {}
  local max = count - 1
  while #res <= max do
    local mapobj = map[ addr + #res ]
    local success
    if mapobj then
      local value = grp.getvalue(mapobj.address)
      if type(value) == 'boolean' then
        value = value and 1 or 0
      if type(value) ~= 'number' then
        alert('invalid value ' .. mapobj.address .. ' ' .. tostring(value))
        value = 0
      success = readvalue(res, value, mapobj.dpt)
    if not success then
      res[ #res + 1 ] = zeroreg
  if #res ~= count then
  return string.char(count * 2) .. table.concat(res)
local function writevalue(obj, data, offset)
  local words = obj.len
  local len = words * 2
  local raw = data:sub(offset, offset + len - 1)
  if #raw < len then
    return
  local buf = {}
  for i = 1, words do
    local word = touint16(raw, i * 2 - 1, byteswap)
    local hex = string.format('%04X', word)
    if wordswap then
      buf[ #buf + 1 ] = hex
      table.insert(buf, 1, hex)
  local hexval = table.concat(buf)
  local dpt = obj.dpt == dt.float16 and dt.int16 or obj.dpt
  local value = busdatatype.decode(hexval, dpt)
  if obj.dpt == dt.float16 then
    value = value / f16mult
  grp.write(obj.address, value)
handlers.readcoils = readbits
handlers.readdiscreteinputs = readbits
handlers.readregisters = readregisters
handlers.readinputregisters = readregisters
handlers.writecoil = function(slaveid, fncode, data)
  if #data ~= 4 then
    return
  if not map or not map[ addr ] then
  local bval = touint16(data, 3) == coilon
  grp.write(map[ addr ], bval, dt.bool)
  return data
handlers.writeregister = function(slaveid, fncode, data)
  if #data ~= 4 then
    return
  local mapobj = map[ addr ]
  if mapobj.len ~= 1 then
  writevalue(mapobj, data, 3)
  return data
handlers.writecoils = function(slaveid, fncode, data)
  if #data < 5 then
    return
  local bytes = touint8(data, 5)
  if #data ~= (bytes + 5) then
    return
  if count == 0 or count > limits.writebits or bytes ~= math.ceil(count / 8) then
  if not map then
  local offset = 6
  local byte = data:byte(offset)
  local bits = 0
    local bval = bit.band(bit.rshift(byte, bits), 1)
    if mapaddr then
      grp.write(mapaddr, bval, dt.bool)
    bits = bits + 1
    if bits == 8 then
      bits = 0
      offset = offset + 1
  return data:sub(1, 4)
handlers.writeregisters = function(slaveid, fncode, data)
  if #data < 5 then
    return
    return
  if count == 0 or count > limits.writeregisters or bytes ~= count * 2 then
  if not map then
    local mapobj = map[ addr + i ]
    if mapobj and not mapobj.readonly then
      local offset = 6 + i * 2
      writevalue(mapobj, data, offset)
exception.tcp = function(sock, hdr, excode)
  local fncode = bit.bor(0x80, hdr:byte(8))
  local resp = hdr:sub(1, 4) ..
    string.char(0, 3) ..
    hdr:sub(7, 7) ..
    string.char(fncode, excode)
  return sock:send(resp)
exception.rtu = function(mbrtu, hdr, excode)
  local fncode = bit.bor(0x80, hdr:byte(2))
  local resp = hdr:sub(1, 1) ..
  return mbrtu:send(resp)
reply.tcp = function(sock, hdr, data)
    string.char(0, #data + 2) ..
    hdr:sub(7, 8) .. data
reply.rtu = function(mbrtu, hdr, data)
  local resp = hdr:sub(1, 2) .. data
local function handler(mode, ctx, hdr, data)
  local slaveid, fncode = hdr:byte(#hdr - 1, #hdr)
  local fnname = fncodes[ fncode ]
  if not fnname then
    return exception[ mode ](ctx, hdr, excodes.illegalfunction)
  local res = handlers[ fnname ](slaveid, fncode, data)
  if type(res) == 'number' then
    return exception[ mode ](ctx, hdr, res)
  elseif type(res) == 'string' then
    return reply[ mode ](ctx, hdr, res)
_M.tcphandler = function(sock)
  local hdr, err = sock:receive(8)
  if not hdr then
    return nil, err
  local len = touint16(hdr, 5) - 2
  local data
  if len <= 0 or len > maxpdu then
    err = 'protocol error'
    data, err = sock:receive(len)
  if not data then
    return nil, err
  return handler('tcp', sock, hdr, data)
_M.rtuhandler = function(mbrtu)
  local data, err = mbrtu:receive()
  if not data then
    return nil, err
  local slaveid = data:byte(1)
  if not mapping[ slaveid ] then
    return
  return handler('rtu', mbrtu, data:sub(1, 2), data:sub(3, #data - 2))
_M.setswap = function(swap)
  byteswap = swap:find('b') ~= nil
  wordswap = swap:find('w') ~= nil
_M.setfloat16precision = function(prec)
  prec = tonumber(prec) or 0
  f16mult = math.pow(10, prec)
local function initobject(obj, dbobj)
  local dpt = obj.datatype or dbobj.datatype
  if type(dpt) == 'string' then
    dpt = dt[ dpt ] or 0
  if type(dpt) == 'number' and dpt >= 1000 then
    dpt = math.floor(dpt / 1000)
  obj.dpt = dpt
  obj.len = dtlens[ dpt ]
  obj.address = dbobj.address
  if not obj.len then
    alert('invalid data type ' .. obj.address .. ' ' .. tostring(dpt))
    return
  return obj
local function initobjects(objects)
  if type(objects) ~= 'table' then
    return
  for addr, obj in pairs(objects) do
    if type(obj) == 'string' then
      obj = { address = obj }
    local dbobj = grp.find(obj.address)
    if dbobj then
      obj = initobject(obj, dbobj)
      alert('missing object ' .. obj.address)
      obj = nil
    objects[ addr ] = obj
_M.setmapping = function(map)
  for _, smap in pairs(map) do
    initobjects(smap.registers)
    initobjects(smap.inputregisters)
  mapping = map
return _M
2a. For Modbus TCP slave create resident script with 0 interval and set object mapping in the table. Remember to create gap in registers for 32 and 64 bit objects.
local mb = require('user.mbslave')
local copas = require('copas')
local socket = require('socket')
local address = '*'
local port = 502
local server = assert(socket.bind(address, port))
mb.setmapping({
    coils = {
      [0] = '0/0/1',
      [1] = '1/1/1',
      [2] = '1/1/2',
    registers = {
      [0] = '1/1/4',
      [1] = '1/1/10',
      [3] = '32/1/6',
      [5] = '32/1/13',
mb.setswap('w')
mb.setfloat16precision(2)
local function handler(sock)
  copas.setErrorHandler(log)
  sock = copas.wrap(sock)
  sock:settimeout(60)
  while true do
    local res, err = mb.tcphandler(sock)
    if not res then
      break
  sock:close()
copas.addserver(server, handler, 60)
copas.loop()
2b. For Modbus RTU slave create resident script with 0 interval and set object mapping in the table. Remember to create gap in registers for 32 and 64 bit objects. Change serial port settings in mbrtu:open as needed.
local mbrtu = require('luamodbus').rtu()
mbrtu:open('/dev/RS485-1', 9600, 'E', 8, 1, 'H')
mbrtu:connect()
mbrtu:setslave('*') -- '*' handles multiple RTU slave IDs
mb.setmapping({
  [1] = {
    coils = {
      [0] = '0/0/1',
      [1] = '1/1/1',
      [2] = '1/1/2',
    registers = {
      [0] = '1/1/4',
      [1] = '1/1/10',
      [3] = '32/1/6',
      [5] = '32/1/13',
mb.setswap('w')
while true do
  mb.rtuhandler(mbrtu)
Hello Daniel.
Thanks for the info, but it doesn't work.
Communication with the Modbus master is not established.
Works for me, paste your script.
And make sure all other modbus scripts are disabled
Hi Daniel, I don't understand this instruction, can you give me more explanation. "Remember to enable/disable resident script after each change."
The master can write and read data from the LM slave?
where can I add the slave address?
In current firmware a resident script with 0 interval must be disabled and then enabled again to load any change made in the script.
In the table where you have ['*'] is place for slave ID. '*' means it will accept requests to any slave ID. You can change it to [1] and then it will be slave 1
Hello Daniel. The script worked very well , thank you very much.
Hello Daniel.
I am getting this message in logs: *nill
What can be?
Adicional,
I need to use 150 registers, but i see in te code that only I can use 125, how can i increase it?
Replace this line:
With this:
copas.setErrorHandler(function(msg)
  if msg ~= nil then
    log(msg)
end)
Hello Daniel.
I chage this line in the resident script, but still showing the same message in logs.
I also see that CPU/IO increases a lot, I'm trying to read 150 objects
Are you sure that the log comes from this script? Check the name of the script in Logs. Just to be sure restart the Modbus script via disable/enable.
As defined by the Modbus standard you can read up to 125 registers at once using a single request. But each devices can have up to 65536 registers.
Hello Daniel.
I did what you told me. But is the same logs massage. How do I read more than 125 registers ?
You can't as modbus standard is defining it, but this is limit for reading 125 at once, you can make several reads with smaller batches.
I can use two diferent script?
A question a Modbus Master can write to me more than 125 registration?, I can have more than 125 register in memory to other modbus master write to me.?
Back to basics Smile This is slave script, it does not read anything. Your master is responsible for reading. In there you define how it reads. Nothing to do with LM.
Hi Daniel
The idea is this. I need that one or more masters can write to me in 150 madbus registers. In other words, I need to create a mapping register with 150 register so that they master can write to me and I can have them available this register to show them in LM. it's possible?
I made myself clear?
You can have up to 65536 registers.
(28.02.2023, 07:02)admin Wrote: You can have up to 65536 registers.
can we test the exported point with LM5?
with the read test !
Trying to make a reading test with Modbus Poll program and the values do not change at all, please see attached.
this is the resident script that I'm using
local mb = require('user.mbtcp')
local address = '*'
local port = 502
mb.setmapping({
  ['1'] = {
    coils = {
      [0] = '0/0/1',
      [1] = '0/0/2',
      [2] = '0/0/3',
      [4] = '0/0/4',
    registers = {
      [0] = '1/1/4',
      [5] = '1/1/6',
mb.setswap('w')
  sock:settimeout(60)
  while true do
    if not res then
      break
  sock:close()
copas.loop()
You can use RTU test. Check if you have any errors in slave script.
(06.03.2023, 14:35)Daniel Wrote: You can use RTU test. Check if you have any errors in slave script.
 Those group addresses should be exported to the Modbus TCP/IP, is that right?
There's no errors