This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Bacnet/ip LM 5 lite
#7
As mentioned before if you want to use read/write in parallel then use direct connection mode. Check if there's another value on your device with a priority lower than 13. Check the result/error when writing (adjust device IP as needed):
Code:
require('bacnet')

bacnet.deviceip = '192.168.0.21'

value = event.getvalue()

res, err = bacnet.write(2, 'analog value', 2070, value, 13)
log(res, err)
Reply


Messages In This Thread
Bacnet/ip LM 5 lite - by Alexander - 18.09.2023, 21:34
RE: Bacnet/ip LM 5 lite - by admin - 19.09.2023, 07:37
RE: Bacnet/ip LM 5 lite - by Alexander - 20.09.2023, 17:09
RE: Bacnet/ip LM 5 lite - by Alexander - 20.09.2023, 18:34
RE: Bacnet/ip LM 5 lite - by admin - 21.09.2023, 05:08
RE: Bacnet/ip LM 5 lite - by Alexander - 21.09.2023, 10:17
RE: Bacnet/ip LM 5 lite - by admin - 21.09.2023, 10:22
RE: Bacnet/ip LM 5 lite - by Alexander - 28.09.2023, 18:47

Forum Jump: