Script change of Bacnet COV settings
Hi.
Im about to create a few Bacnet COV points on a large number of Wiser4KNX.
When the points are created they start with a send on change of 1, I need this to be 0.5, can this be scripted of do I need to manually change this?
Robert.
Use this:
--Best way is to tag your objects with a specific tag for each different COV value and then run this script once:
covincr = 0.1
tag = 'mycovtag1'
db:query('UPDATE objects SET covincr=? WHERE id IN (SELECT object FROM objecttags WHERE tag=?)', covincr, tag)
covincr = 0.5
tag = 'mycovtag2'
os.execute('/etc/init.d/bacnet restart')
script.disable(_SCRIPTNAME)
--or
covincr = 0.1
db:query('UPDATE objects SET covincr=? WHERE export = 1', covincr)