This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Calculation of power consumed in the Valle, Llano and Punta periods of the Spanish el
#1
The Spanish electricity rate with the PVPC establishes three time periods, namely:

Punta hours : 10:00 - 14:00 and 18:00 - 22:00 from Monday to Friday.
Llano hours 8:00 - 10:00, 14:00 - 18:00 and 22:00 - 00:00 from Monday to Friday.
Valle hours 00:00 - 08:00 from Monday to Friday

Holidays and weekends are 24 valle hours.

I have an object with the total instantaneous active power of the installation.

Likewise I have an object with the total power consumed.

How could I calculate the power consumed in each time slot?

That is to say:

Power consumed in:
Rush hour (10:00 - 14:00) =
Rush hour (18:00 - 22:00) =
etc

This way it would allow me to easily visualize what time I have the most consumption.

Thank you.

Greetings.
Reply
#2
You can use trends in counter mode mapped to the total power object. Set resolution to 1 hour to simplify the calculation. Then trends library functions can be used to query the data and calculate total consumption for different time slots.
Reply


Forum Jump: