Threads: 3
I'm using a Intesis router ip-mstp.
192.168.100.246
I get read bacnet clients
246 - 192.168.100.246 -router
50001 - 192.168.100.246 - device mstp
But when I try to read objects I always have the same error: unknown object,
require('bacnet')
bacnet.deviceip = '192.168.100.246'
device_id = 50001
value,err = bacnet.readvalue(device_id, 'analog value',1086)
log(err)
[size=1][size=1]*
[/size][/size]
Install YABE and check what objects are discovered. Some extra configuration might be needed on the BACnet router.
Threads: 3
15.11.2023, 13:23
(This post was last modified: 15.11.2023, 13:33 by AngelesTR.)
Hi:
With YABE I have managed to discover all the variables
What can i do now?
In Yabe right click Devices, select Add device. There under BACnet/IP over Udp click Add. For testing purposes you can enable BACnet server on LM. It should appear in Yabe once it's configured correctly.
Threads: 3
15.11.2023, 13:34
(This post was last modified: 15.11.2023, 13:42 by AngelesTR.)
Yes ,yes the problem was the port....
If I can discover the values with YABE there is no reason not to discover them with LM, right?
Thanks in advance...
It should work on LM if correct parameters are provided. Show a screenshot from Yabe with discovered devices and objects.
Threads: 3
15.11.2023, 13:51
(This post was last modified: 15.11.2023, 13:54 by AngelesTR.)
sorry but I don't know how insert an imagen in the Post.
yabe shows this tree:
udp:47808
device 246-192.168.100.246:47808 /this is the router
device-50001 - 90 / this is the device SMTP
At this moment reading devices under routers is not supported. We will look into adding support for this in the next firmware.
Threads: 3
And when you think it will be possible. I have a serious problem with that at this moment.
Best Regards
New firmware will only be available in several months time.
It would be very helpful if you could provide a Wireshark packet dump when accessing the MS/TP device via Yabe.
1. Install and run Wireshark
2. Set filter to udp.port==0xBAC0
3. Run Yabe and click at least one of the MS/TP objects in the discovered object list
4. Click Stop in Wireshark and click File > Export Specified Packets, save the packet dump with default settings
