This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Trend clean
#9
This example will change all valid trend values by x2. Recommended way of testing is to create a new trend log with the same parameters as the source.

Code:
infile = '/tmp/trends/t1.trend'
outfile = '/tmp/trends/t7.trend'

function adjust(value)
  value = value * 2
  return value
end

ffi = require('ffi')

function stringtodouble(chunk)
  local dbl = ffi.new('double[1]')
  ffi.copy(dbl, chunk, 8)
  return dbl[ 0 ]
end

function doubletostring(val)
  local dbl = ffi.new('double[1]')
  dbl[ 0 ] = val
  return ffi.string(dbl, 8)
end

info = require('rrd').info(infile)

data = io.readfile(infile)
offset = info.header_size

buf = { data:sub(1, offset) }

while true do
  chunk = data:sub(offset + 1, offset + 8)

  if #chunk == 8 then
    value = stringtodouble(chunk)

    -- skip NaN (empty/undefined value)
    if value == value then
      value = adjust(value)
    end

    buf[ #buf + 1 ] = doubletostring(value)
  else
    break
  end

  offset = offset + 8
end

data = table.concat(buf)
io.writefile(outfile, data)

For counter type the editing is trickier. The stored value is not the actual counter value but a per-second change rate. This example will log the maximum of all stored values without writing to a different trend log file. You can use this value for replacement in the previous script.
Code:
infile = '/tmp/trends/t1.trend'

max = 0

function check(value)
  max = math.max(max, value)
end

ffi = require('ffi')

function stringtodouble(chunk)
  local dbl = ffi.new('double[1]')
  ffi.copy(dbl, chunk, 8)
  return dbl[ 0 ]
end

info = require('rrd').info(infile)

data = io.readfile(infile)
offset = info.header_size

while true do
  chunk = data:sub(offset + 1, offset + 8)

  if #chunk == 8 then
    value = stringtodouble(chunk)

    -- skip NaN (empty/undefined value)
    if value == value then
      check(value)
    end
  else
    break
  end

  offset = offset + 8
end

log(max)

Note that when replacing values you should not use direct comparison (==) for floating point values due to possible rounding errors.
Reply


Messages In This Thread
Trend clean - by domotiqa - 22.11.2023, 07:12
RE: Trend clean - by Daniel - 22.11.2023, 08:42
RE: Trend clean - by domotiqa - 22.11.2023, 08:51
RE: Trend clean - by Daniel - 22.11.2023, 08:54
RE: Trend clean - by domotiqa - 22.11.2023, 08:59
RE: Trend clean - by admin - 22.11.2023, 09:01
RE: Trend clean - by domotiqa - 22.11.2023, 09:25
RE: Trend clean - by domotiqa - 15.12.2023, 07:44
RE: Trend clean - by admin - 15.12.2023, 10:47
RE: Trend clean - by domotiqa - 19.12.2023, 08:23
RE: Trend clean - by domotiqa - 19.12.2023, 16:39

Forum Jump: