Smartlogger Huawai
Hi, I can't read modbus register on this Smartlogger with TCP connection, device address: 0 (fixed).
I created the attached modbus profiles (40*** formart as in the pdf and ***),  mapped register with virtual objects, but I receive no data.
on the contrary, with Modbus Tool I can read everything.
Can you help me?
Peppe
.pdf   SmartLogger ModBus Interface Definitions.pdf (Size: 748.52 KB / Downloads: 4)
.json   SMARTLOGGER-HUAWEI ho.json (Size: 1.23 KB / Downloads: 3)
.json   SMARTLOGGER-HUAWEI.json (Size: 1.25 KB / Downloads: 3)
Usually the starting number 4 indicates the function code so it should be ignored in the register address. What do you get when running Read test?
(28.06.2024, 08:54)admin Wrote: Usually the starting number 4 indicates the function code so it should be ignored in the register address. What do you get when running Read test?
I can't run read test because I can't select device address 0.... it's starting from 1
There is no such thing in modbus as addressee 0, try 254 or 255
(28.06.2024, 09:27)Daniel Wrote: There is no such thing in modbus as addressee 0, try 254 or 255
you are right, sorry....  the correct id is 50.
By the way, now I can read almost all register in the profile but KW value registers: they are both on 0 value.
if I run a read test they give me an int value.
.json   SMARTLOGGER-HUAWEI.json (Size: 1.34 KB / Downloads: 4)
Add "datatype": "uint32" to relevant profile entries. You should also add value_multiplier where applicable. But in this case bus_datatype should be a floating point value, not uint32.
ALL RIGHT! Thanks