Threads: 2
I have a requirement to assign KNX group addresses to individual parameters on the Airconditioning widget
I can scroll and see on some of the fields the required group addresses, on other parameters (eg operation mode) I can not see any of the required group addresses
Why is this and how do I resolve?
Threads: 30
Widgets filter groups which have correct datatype for a particular object, it means you must convert it.
Threads: 2
Thanks Daniel
2 questions.
Does Logic Machine automatically update datatypes from KNX if they are changed in ETS, or do i have to manually reimport
Is there a data dictionary of what datatype is valid for each field in a widget?
Threads: 30
1 no you should remove such group and import ets project or just change manually in object in LM.
2. Not really but you can ask which one you are not sure.
Threads: 2
I've just reallocated the dpt types for HVAC Control mode 20.105 however it still doesnt show up as an object i can reference in Mosaic for the "climate mode status object"
Threads: 30