Stop execution of KNX secuence
Hello from Spain,
i have a script with a secuence in KNX, using "os.sleep(t)" to do a delay between telegrams. It works well, but in any case, the secuence duration is 4-5 minutes.
¿How can i do to stop the secuence in the middle of execution? Any "break" or "exit" or "kill" exception to stop the script.
os.sleep(23)
  grp.write('0/0/39', 0)
  grp.write('0/0/53', 0)
  grp.write('0/0/56', 0)
  grp.write('0/0/58', 0)
  grp.write('0/0/40', 0)
  grp.write('0/0/62', 0)
  grp.write('0/0/47', 0)
  grp.write('0/0/41', 1)
  grp.write('0/0/7', 1)
  grp.write('0/5/8', 100)
  grp.write('0/0/29', 1)
  grp.write('0/0/33', 1)
  os.sleep(14)
  grp.write('0/0/41', 0)
  grp.write('0/0/7', 0)
  grp.write('0/0/29', 0)
  grp.write('0/0/33', 0)
  grp.write('0/0/38', 1)
  grp.write('0/0/59', 1)
  grp.write('0/0/60', 1)
  grp.write('0/0/61', 1)
  os.sleep(39)
  grp.write('0/5/8', 0)
  grp.write('0/0/38', 0)
  grp.write('0/0/59', 0)
  grp.write('0/0/60', 0)
  grp.write('0/0/61', 0)
Thanks!
Iván.
You can use an object or a storage variable as a status, then check this status after each sleep:
os.sleep(23)
if not grp.getvalue('1/1/1') then
  return
(31.08.2017, 11:29)admin Wrote: You can use an object or a storage variable as a status, then check this status after each sleep:
os.sleep(23)
 return
Thanks admin!!
It works! The inconvenience is that i have to copy that a lot of times in the code, but it works.
Ivan.
You can prepare some table with values and then iterate over it with some loop.This is only a little inspirationWink
pause = 14 -- seconds
statusGA = '1/1/1'
sequence = {
{grp = '1/2/3', val = 1 },
{grp = '1/2/6', val = 100 }
for _, scene in ipairs(sequence) do
grp.write(scene.grp, scene.val)
if grp.getvalue(statusGA) == false then break end
os.sleep(pause)
Hi Buuuudzik,
Check your sample (:
statusGA is a address (string) and not a value so will never be false (bool)
Thanks, yes I've updated the above scriptWink