Universal Modbus TCP/RTU Slave - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Universal Modbus TCP/RTU Slave (/showthread.php?tid=4288) |
RE: Universal Modbus TCP/RTU Slave - djaval - 27.03.2024 (26.02.2024, 09:08)Daniel Wrote: This is how it meant to work. You need to convert it back to float on master device. Hi! Yes, it works. Not a big problem to convert back to float on master device, but just to clarify. Is it possible to make pure float register (either it can be little or big endian)? RE: Universal Modbus TCP/RTU Slave - admin - 28.03.2024 float32 data type is handled as is without any conversion. The script can be modified to convert float16 to float32 instead of int16. Edit: script has been updated with optional conversion of float16 to float32: https://kb.logicmachine.net/integration/modbus-rtu-tcp-slave/ RE: Universal Modbus TCP/RTU Slave - Krstfr2k - 12.06.2024 How do i set up the script to use slave id 1 on the first RS-485 port and slave id 2 on the second RS-485 port on an LM5 Lite? RE: Universal Modbus TCP/RTU Slave - admin - 12.06.2024 Create two separate scripts, one for each port. RE: Universal Modbus RTU - Ranjeet - 14.06.2024 I am Using Daikin Ac and Ac Guy Given me address and holding register ID. So query is that when I'm triggering from Logic Machine not getting response from AC. even i used json file. RE: Universal Modbus TCP/RTU Slave - Daniel - 14.06.2024 This thread is for modbus slave and you are using master so if you have issues create dedicated topic for your case please. RE: Universal Modbus TCP/RTU Slave - Ranjeet - 11.07.2024 Hi Sir, When I am doing read test in Modbus in Logic Machine then it is showing me this number, what does it mean? I have Attached Sceenshot RE: Universal Modbus TCP/RTU Slave - Daniel - 11.07.2024 It is what the text says, result of the read request. RE: Universal Modbus TCP/RTU Slave - Ranjeet - 12.07.2024 Thanks For Reply sir I want to Know that how to understand this result and What it means RE: Universal Modbus TCP/RTU Slave - admin - 12.07.2024 Check the register description in the device documentation. RE: Universal Modbus TCP/RTU Slave - imprashant - 16.04.2025 We have 5 Zones in our project and each zone has an Automation DB having KNX Actuators and a KNX keypad. So now we have to implement Auto/Manual logic in that way that if we press the button on KNX keypad the DB will go on the manual mode, it means now we are only able to control the DB devices (KNX Actuators) with keypad only and no command can be executed from the SCADA system until we remove the Manual mode by pressing the Auto mode key on the KNX keypad. This Auto/Manual logic is to be implemented for all the 5 Zones. Is it possible to make different resident script for different zone in MODBUS RTU so that we can disable the communication of particular zone by just disabling the resident script of that particular zone. We are using one LM5 as MODBUS RTU Slave for all 5 Zones. RE: Universal Modbus TCP/RTU Slave - admin - 16.04.2025 Multiple resident scripts can't share the same RS-485 port. It should be enough just to block writing as needed. Replace the whole handlers.writeregister function with this, modify writeallowed logic as needed. Code: local function writeallowed(slaveid)
if slaveid == 1 then
return grp.getvalue('1/1/1')
elseif slaveid == 2 then
return grp.getvalue('1/1/2')
handlers.writeregister = function(slaveid, fncode, data)
if #data ~= 4 then
return
local addr = touint16(data, 1)
local map = getmapping(slaveid, fncode)
if not map or not map[ addr ] then
return excodes.illegaldataaddress
local mapobj = map[ addr ]
if mapobj.len ~= 1 then
if writeallowed(slaveid) then
writevalue(mapobj, data, 3)
return data
endReplace the whole handlers.writeregisters function with this. Code: handlers.writeregisters = function(slaveid, fncode, data)
if #data < 5 then
return
local count = touint16(data, 3)
local bytes = touint8(data, 5)
if #data ~= (bytes + 5) then
return
if count == 0 or count > limits.writeregisters or bytes ~= count * 2 then
if not map then
for i = 0, (count - 1) do
local mapobj = map[ addr + i ]
if mapobj and not mapobj.readonly then
local offset = 6 + i * 2
writevalue(mapobj, data, offset)
return data:sub(1, 4)
endRE: Universal Modbus TCP/RTU Slave - imprashant - 18.04.2025 Hi, I have done the changes in the mbslave (user library script). But still I didn't understand how will I disable one Zone to communicate with the SCADA over modbus rtu. Do I need to make some changes in resident script as well. Please guide. RE: Universal Modbus TCP/RTU Slave - imprashant - 21.04.2025 (18.04.2025, 15:16)imprashant Wrote: Hi, I have done the changes in the mbslave (user library script). But still I didn't understand how will I disable one Zone to communicate with the SCADA over modbus rtu. Do I need to make some changes in resident script as well. Please guide. Previously the script I was using was working but sometimes I have to send command 2-3 times from Modscan in order to execute command in LM5. The script I was using: local mb = require('user.mbslave') local mbrtu = require('luamodbus').rtu() mbrtu:open('/dev/RS485-1', 9600, 'N', 8, 1, 'H') mbrtu:connect() mbrtu:setslave('*') -- Accept multiple RTU slave IDs mb.setswap('w') mb.setfloat16precision(2) local ga1 = '0/0/11' --zone 1 enable/disable local ga2 = '0/0/12' --zone 2 enable/disable local current_mapping = nil -- Predefine mappings for easy reuse local mapping1 = { [1] = { coils = { [0] = '0/0/1', }, registers = { [0] = '0/0/2', } } } local mapping2 = { [1] = { coils = { [1] = '0/0/3', }, registers = { [1] = '0/0/4', } } } while true do local val1 = grp.getvalue(ga1) local val2 = grp.getvalue(ga2) if not val1 and current_mapping ~= "mapping1" then mb.setmapping(mapping1) current_mapping = "mapping1" log("Applied Mapping 1") elseif not val2 and current_mapping ~= "mapping2" then mb.setmapping(mapping2) current_mapping = "mapping2" log("Applied Mapping 2") end mb.rtuhandler(mbrtu) os.sleep(1) -- small delay to prevent CPU hogging end RE: Universal Modbus TCP/RTU Slave - admin - 22.04.2025 The previous solution is meant to be used with multiple slave IDs. Writing to slave ID 1 is allowed when 1/1/1 is true, writing to slave ID 2 is allowed when 1/1/2 is true. writeallowed should be modified as needed. Alternative solution is to add logic AND gates to mapped group addresses. Updated user library: Code: local _M = {}
local byteswap, wordswap
local f16mult = 1
local f16float = false
local mapping = {}
local exception = {}
local reply = {}
local fncodes = {
[1] = 'readcoils',
[2] = 'readdiscreteinputs',
[3] = 'readregisters',
[4] = 'readinputregisters',
[5] = 'writecoil',
[6] = 'writeregister',
[15] = 'writecoils',
[16] = 'writeregisters',
local mapfncodes = {
[1] = 'coils',
[2] = 'discreteinputs',
[3] = 'registers',
[4] = 'inputregisters',
[5] = 'coils',
[6] = 'registers',
[15] = 'coils',
[16] = 'registers',
local dtlens = {
[ dt.bool ] = 1,
[ dt.bit4 ] = 1,
[ dt.int8 ] = 1,
[ dt.uint8 ] = 1,
[ dt.int16 ] = 1,
[ dt.uint16 ] = 1,
[ dt.float16 ] = 1,
[ dt.int32 ] = 2,
[ dt.uint32 ] = 2,
[ dt.float32 ] = 2,
[ dt.int64 ] = 4,
local maxpdu = 253
local maxaddr = 0x10000
local coilon = 0xFF00
local limits = {
readbits = 2000,
writebits = 1968,
readregisters = 125,
writeregisters = 123,
local excodes = {
illegalfunction = 1,
illegaldataaddress = 2,
illegaldatavalue = 3,
serverdevicefailure = 4,
acknowledge = 5,
serverdevicebusy = 6,
negativeacknowledge = 7,
memoryparityerror = 8,
gatewaypathunavailable = 10,
gatewaytargetdevicefailed = 11,
local handlers = {}
local function touint8(buf, off)
return buf:byte(off)
local function touint16(buf, off, swap)
local b1, b2 = buf:byte(off, off + 1)
if swap then
b1, b2 = b2, b1
return b1 * 0x100 + b2
local function getmapping(slaveid, fncode)
local mapfncode = mapfncodes[ fncode ]
local slave = mapping[ slaveid ]
if not slave then
slave = mapping['*']
if slave then
return slave[ mapfncode ]
local function readbits(slaveid, fncode, data)
if #data ~= 4 then
return
if count == 0 or count > limits.readbits then
elseif (addr + count) > maxaddr then
if not map then
local res = {}
local bits, byte = 0, 0
local mapaddr = map[ addr + i ]
if mapaddr then
local bval = grp.getvalue(mapaddr)
if toboolean(bval) then
byte = byte + bit.lshift(1, bits)
bits = bits + 1
if bits == 8 then
res[ #res + 1 ] = string.char(byte)
bits, byte = 0, 0
if bits ~= 0 then
return string.char(#res) .. table.concat(res)
local zeroreg = string.char(0, 0)
local function readvalue(res, value, dpt)
if dpt == dt.float16 then
if f16float then
dpt = dt.float32
value = value * f16mult
dpt = dt.int16
local enc = busdatatype.encode(value, dpt)
if not enc.dataraw then
return
local raw = enc.dataraw
if #raw % 2 == 1 then
local pad = value < 0 and 0xFF or 0
raw = string.char(pad) .. raw
local words = #raw / 2
local offset = #res
for i = 1, words do
local word = raw:sub(i * 2 - 1, i * 2)
if byteswap then
word = word:sub(2, 2) .. word:sub(1, 1)
if wordswap then
res[ offset + i ] = word
res[ offset + 1 + words - i ] = word
return true
local function readregisters(slaveid, fncode, data)
if #data ~= 4 then
return
if count == 0 or count > limits.readregisters then
if not map then
local res = {}
local max = count - 1
while #res <= max do
local mapobj = map[ addr + #res ]
local success
if mapobj then
local value = grp.getvalue(mapobj.address)
if type(value) == 'boolean' then
value = value and 1 or 0
if type(value) ~= 'number' then
alert('invalid value ' .. mapobj.address .. ' ' .. tostring(value))
value = 0
success = readvalue(res, value, mapobj.dpt)
if not success then
res[ #res + 1 ] = zeroreg
if #res ~= count then
return string.char(count * 2) .. table.concat(res)
local function writevalue(obj, data, offset)
local words = obj.len
local len = words * 2
local raw = data:sub(offset, offset + len - 1)
if #raw < len then
return
local buf = {}
for i = 1, words do
local word = touint16(raw, i * 2 - 1, byteswap)
local hex = string.format('%04X', word)
if wordswap then
buf[ #buf + 1 ] = hex
table.insert(buf, 1, hex)
local hexval = table.concat(buf)
local dpt = obj.dpt
dpt = f16float and dt.float32 or dt.int16
local value = busdatatype.decode(hexval, dpt)
if obj.dpt == dt.float16 and not f16float then
value = value / f16mult
_M.write(obj.address, value)
handlers.readcoils = readbits
handlers.readdiscreteinputs = readbits
handlers.readregisters = readregisters
handlers.readinputregisters = readregisters
handlers.writecoil = function(slaveid, fncode, data)
if #data ~= 4 then
return
local bval = touint16(data, 3) == coilon
_M.write(map[ addr ], bval, dt.bool)
return data
if #data ~= 4 then
return
return data
handlers.writecoils = function(slaveid, fncode, data)
if #data < 5 then
return
return
if count == 0 or count > limits.writebits or bytes ~= math.ceil(count / 8) then
if not map then
local offset = 6
local byte = data:byte(offset)
local bits = 0
local bval = bit.band(bit.rshift(byte, bits), 1)
if mapaddr then
_M.write(mapaddr, bval, dt.bool)
bits = bits + 1
if bits == 8 then
bits = 0
offset = offset + 1
if #data < 5 then
return
return
if not map then
exception.tcp = function(sock, hdr, excode)
local fncode = bit.bor(0x80, hdr:byte(8))
local resp = hdr:sub(1, 4) ..
string.char(0, 3) ..
hdr:sub(7, 7) ..
string.char(fncode, excode)
return sock:send(resp)
exception.rtu = function(mbrtu, hdr, excode)
local fncode = bit.bor(0x80, hdr:byte(2))
local resp = hdr:sub(1, 1) ..
return mbrtu:send(resp)
reply.tcp = function(sock, hdr, data)
string.char(0, #data + 2) ..
hdr:sub(7, 8) .. data
reply.rtu = function(mbrtu, hdr, data)
local resp = hdr:sub(1, 2) .. data
local function handler(mode, ctx, hdr, data)
local slaveid, fncode = hdr:byte(#hdr - 1, #hdr)
local fnname = fncodes[ fncode ]
if not fnname then
return exception[ mode ](ctx, hdr, excodes.illegalfunction)
local res = handlers[ fnname ](slaveid, fncode, data)
if type(res) == 'number' then
return exception[ mode ](ctx, hdr, res)
elseif type(res) == 'string' then
return reply[ mode ](ctx, hdr, res)
_M.tcphandler = function(sock)
local hdr, err = sock:receive(8)
if not hdr then
return nil, err
local len = touint16(hdr, 5) - 2
local data
if len <= 0 or len > maxpdu then
err = 'protocol error'
data, err = sock:receive(len)
if not data then
return nil, err
return handler('tcp', sock, hdr, data)
_M.rtuhandler = function(mbrtu)
local data, err = mbrtu:receive()
if not data then
return nil, err
local slaveid = data:byte(1)
if not mapping[ slaveid ] then
return
return handler('rtu', mbrtu, data:sub(1, 2), data:sub(3, #data - 2))
_M.setswap = function(swap)
byteswap = swap:find('b') ~= nil
wordswap = swap:find('w') ~= nil
_M.setfloat16precision = function(prec)
prec = tonumber(prec) or 0
f16mult = math.pow(10, prec)
_M.setfloat16mode = function(mode)
f16float = mode == 'float'
dtlens[ dt.float16 ] = f16float and 2 or 1
local function initobject(obj, dbobj)
local dpt = obj.datatype or dbobj.datatype
if type(dpt) == 'string' then
dpt = dt[ dpt ] or 0
if type(dpt) == 'number' and dpt >= 1000 then
dpt = math.floor(dpt / 1000)
obj.dpt = dpt
obj.len = dtlens[ dpt ]
obj.address = dbobj.address
if not obj.len then
alert('invalid data type ' .. obj.address .. ' ' .. tostring(dpt))
return
return obj
local function initobjects(objects)
if type(objects) ~= 'table' then
return
for addr, obj in pairs(objects) do
if type(obj) == 'string' then
obj = { address = obj }
local dbobj = grp.find(obj.address)
if dbobj then
obj = initobject(obj, dbobj)
alert('missing object ' .. obj.address)
obj = nil
objects[ addr ] = obj
_M.write = grp.write
_M.setmapping = function(map)
for _, smap in pairs(map) do
initobjects(smap.registers)
initobjects(smap.inputregisters)
mapping = map
return _MResident script example: Code: local mb = require('user.mbslave')
mbrtu:open('/dev/RS485-1', 9600, 'E', 8, 1, 'H')
mbrtu:connect()
mbrtu:setslave('*') -- '*' handles multiple RTU slave IDs
mb.setswap('w')
mb.setmapping({
[1] = {
coils = {
[0] = '0/0/1',
[1] = '0/0/3',
[2] = '0/0/4',
discreteinputs = {
[0] = '1/0/1',
[1] = '1/0/3',
[2] = '1/0/4',
registers = {
[0] = '1/1/4',
[1] = '1/1/10',
[3] = '32/1/6',
[5] = '32/1/13',
inputregisters = {
[0] = '2/1/4',
[1] = '2/1/10',
local gates = {
['0/0/3'] = '32/0/1',
['1/0/1'] = '32/0/2',
['1/0/3'] = '32/0/2',
['1/0/4'] = '32/0/3',
mb.write = function(addr, value, dt)
local gate = gates[ addr ]
if not gate or grp.getvalue(gate) then
grp.write(addr, value, dt)
while true do
endIn gates table key (left side) is mapped group address and value (right side) is controlling gate object. Write to the given mapped group address will only happen if the gate value is true. Writing to group addresses without a gate group address is always allowed. RE: Universal Modbus TCP/RTU Slave - imprashant - 22.04.2025 Hi, Thanks for sharing. It is working fine for the coils i.e 1 bit object. But we have holding registers as well that we are using for scene control in which we are sending 0,1 and 2 value from the same group address. How in the above script we can use gate function for the holding registers. registers = { [1] = '6/3/6', [2] = '6/0/10', [3] = '6/0/11', [4] = '6/2/6',- [5] = '6/2/7', }, RE: Universal Modbus TCP/RTU Slave - admin - 22.04.2025 gates table is shared, it works the same for coils and registers. RE: Universal Modbus TCP/RTU Slave - judgment - 14.08.2025 hi please help with this script. I am trying to test it only with one holding register but its not giving any result. no error either. User library copied. LM firmware 20240426. Reading this signle register from modbus tab works fine. Code: local mb = require('user.mbslave')
mbrtu:connect()
mb.setmapping({
[1] = {
coils = {
registers = {
[4353] = '5/1/0',
mb.setswap('w')
while true do
endRE: Universal Modbus TCP/RTU Slave - Daniel - 14.08.2025 Make sure that RS485-1 is not used anywhere else. It might be enabled on modbus tab(Modbus settings) RE: Universal Modbus TCP/RTU Slave - admin - 14.08.2025 Are you trying to read a Modbus device from LM? If so you need to create a profile. Use this: https://forum.logicmachine.net/showthread.php?tid=5911 |