Universal Modbus TCP/RTU Slave
#61
(26.02.2024, 09:08)Daniel Wrote: This is how it meant to work. You need to convert it back to float on master device.
mb.setfloat16precision(2) sets how float16 is converted to integer. By default it's 2 decimals (0.01 precision). Change 2 to 0 to convert to integer without any decimals.
Hi! Yes, it works. Not a big problem to convert back to float on master device, but just to clarify. Is it possible to make pure float register (either it can be little or big endian)?
float32 data type is handled as is without any conversion. The script can be modified to convert float16 to float32 instead of int16.
Edit: script has been updated with optional conversion of float16 to float32: https://kb.logicmachine.net/integration/...tcp-slave/
How do i set up the script to use slave id 1 on the first RS-485 port and slave id 2 on the second RS-485 port on an LM5 Lite?
Create two separate scripts, one for each port.
I am Using Daikin Ac and Ac Guy Given me address and holding register ID. So query is that when I'm triggering from Logic Machine not getting response from AC. even i used json file.
This thread is for modbus slave and you are using master so if you have issues create dedicated topic for your case please.
Hi Sir,
When I am doing read test in Modbus in Logic Machine then it is showing me this number, what does it mean?
I have Attached Sceenshot
It is what the text says, result of the read request.
Thanks For Reply
sir I want to Know that how to understand this result and What it means
Check the register description in the device documentation.
We have 5 Zones in our project and each zone has an Automation DB having KNX Actuators and a KNX keypad.
So now we have to implement Auto/Manual logic in that way that if we press the button on KNX keypad the DB will go on the manual mode, it means now we are only able to control the DB devices (KNX Actuators) with keypad only and no command can be executed from the SCADA system until we remove the Manual mode by pressing the Auto mode key on the KNX keypad.
This Auto/Manual logic is to be implemented for all the 5 Zones.
Is it possible to make different resident script for different zone in MODBUS RTU so that we can disable the communication of particular zone by just disabling the resident script of that particular zone. We are using one LM5 as MODBUS RTU Slave for all 5 Zones.
Multiple resident scripts can't share the same RS-485 port. It should be enough just to block writing as needed.
Replace the whole handlers.writeregister function with this, modify writeallowed logic as needed.
local function writeallowed(slaveid)
  if slaveid == 1 then
    return grp.getvalue('1/1/1')
  elseif slaveid == 2 then
    return grp.getvalue('1/1/2')
handlers.writeregister = function(slaveid, fncode, data)
  if #data ~= 4 then
    return
  local addr = touint16(data, 1)
  local map = getmapping(slaveid, fncode)
  if not map or not map[ addr ] then
    return excodes.illegaldataaddress
  local mapobj = map[ addr ]
  if mapobj.len ~= 1 then
  if writeallowed(slaveid) then
    writevalue(mapobj, data, 3)
  return data
Replace the whole handlers.writeregisters function with this.
handlers.writeregisters = function(slaveid, fncode, data)
  if #data < 5 then
    return
  local count = touint16(data, 3)
  local bytes = touint8(data, 5)
  if #data ~= (bytes + 5) then
    return
  if count == 0 or count > limits.writeregisters or bytes ~= count * 2 then
  if not map then
    for i = 0, (count - 1) do
      local mapobj = map[ addr + i ]
      if mapobj and not mapobj.readonly then
        local offset = 6 + i * 2
        writevalue(mapobj, data, offset)
  return data:sub(1, 4)
Hi, I have done the changes in the mbslave (user library script). But still I didn't understand how will I disable one Zone to communicate with the SCADA  over modbus rtu. Do I need to make some changes in resident script as well. Please guide.
(18.04.2025, 15:16)imprashant Wrote: Hi, I have done the changes in the mbslave (user library script). But still I didn't understand how will I disable one Zone to communicate with the SCADA  over modbus rtu. Do I need to make some changes in resident script as well. Please guide.
Previously the script I was using was working but sometimes I have to send command 2-3 times from Modscan in order to execute command in LM5. The script I was using:
local mb = require('user.mbslave')
local mbrtu = require('luamodbus').rtu()
mbrtu:open('/dev/RS485-1', 9600, 'N', 8, 1, 'H')
mbrtu:connect()
mbrtu:setslave('*') -- Accept multiple RTU slave IDs
mb.setswap('w')
local ga1 = '0/0/11' --zone 1 enable/disable
local ga2 = '0/0/12' --zone 2 enable/disable
local current_mapping = nil
-- Predefine mappings for easy reuse
local mapping1 = {
    [1] = {
        coils = {
            [0] = '0/0/1',
        registers = {
            [0] = '0/0/2',
local mapping2 = {
    [1] = {
        coils = {
            [1] = '0/0/3',
        registers = {
            [1] = '0/0/4',
while true do
    local val1 = grp.getvalue(ga1)
    local val2 = grp.getvalue(ga2)
    if not val1 and current_mapping ~= "mapping1" then
        mb.setmapping(mapping1)
        current_mapping = "mapping1"
        log("Applied Mapping 1")
    elseif not val2 and current_mapping ~= "mapping2" then
        mb.setmapping(mapping2)
        current_mapping = "mapping2"
        log("Applied Mapping 2")
    mb.rtuhandler(mbrtu)
    os.sleep(1) -- small delay to prevent CPU hogging
The previous solution is meant to be used with multiple slave IDs. Writing to slave ID 1 is allowed when 1/1/1 is true, writing to slave ID 2 is allowed when 1/1/2 is true. writeallowed should be modified as needed.
Alternative solution is to add logic AND gates to mapped group addresses.
Updated user library:
local _M = {}
local byteswap, wordswap
local f16mult = 1
local f16float = false
local mapping = {}
local exception = {}
local reply = {}
local fncodes = {
  [1] = 'readcoils',
  [2] = 'readdiscreteinputs',
  [3] = 'readregisters',
  [4] = 'readinputregisters',
  [5] = 'writecoil',
  [6] = 'writeregister',
  [15] = 'writecoils',
  [16] = 'writeregisters',
local mapfncodes = {
  [1] = 'coils',
  [2] = 'discreteinputs',
  [3] = 'registers',
  [4] = 'inputregisters',
  [5] = 'coils',
  [6] = 'registers',
  [15] = 'coils',
  [16] = 'registers',
local dtlens = {
  [ dt.bool ] = 1,
  [ dt.bit4 ] = 1,
  [ dt.int8 ] = 1,
  [ dt.uint8 ] = 1,
  [ dt.int16 ] = 1,
  [ dt.uint16 ] = 1,
  [ dt.float16 ] = 1,
  [ dt.int32 ] = 2,
  [ dt.uint32 ] = 2,
  [ dt.float32 ] = 2,
  [ dt.int64 ] = 4,
local maxpdu = 253
local maxaddr = 0x10000
local coilon = 0xFF00
local limits = {
  readbits = 2000,
  writebits = 1968,
  readregisters = 125,
  writeregisters = 123,
local excodes = {
  illegalfunction = 1,
  illegaldataaddress = 2,
  illegaldatavalue = 3,
  serverdevicefailure = 4,
  acknowledge = 5,
  serverdevicebusy = 6,
  negativeacknowledge = 7,
  memoryparityerror = 8,
  gatewaypathunavailable = 10,
  gatewaytargetdevicefailed = 11,
local handlers = {}
local function touint8(buf, off)
  return buf:byte(off)
local function touint16(buf, off, swap)
  local b1, b2 = buf:byte(off, off + 1)
  if swap then
    b1, b2 = b2, b1
  return b1 * 0x100 + b2
local function getmapping(slaveid, fncode)
  local mapfncode = mapfncodes[ fncode ]
  local slave = mapping[ slaveid ]
  if not slave then
    slave = mapping['*']
  if slave then
    return slave[ mapfncode ]
local function readbits(slaveid, fncode, data)
  if #data ~= 4 then
    return
  if count == 0 or count > limits.readbits then
  elseif (addr + count) > maxaddr then
  if not map then
  local res = {}
  local bits, byte = 0, 0
    local mapaddr = map[ addr + i ]
    if mapaddr then
      local bval = grp.getvalue(mapaddr)
      if toboolean(bval) then
        byte = byte + bit.lshift(1, bits)
    bits = bits + 1
    if bits == 8 then
      res[ #res + 1 ] = string.char(byte)
      bits, byte = 0, 0
  if bits ~= 0 then
  return string.char(#res) .. table.concat(res)
local zeroreg = string.char(0, 0)
local function readvalue(res, value, dpt)
  if dpt == dt.float16 then
    if f16float then
      dpt = dt.float32
      value = value * f16mult
      dpt = dt.int16
  local enc = busdatatype.encode(value, dpt)
  if not enc.dataraw then
    return
  local raw = enc.dataraw
  if #raw % 2 == 1 then
    local pad = value < 0 and 0xFF or 0
    raw = string.char(pad) .. raw
  local words = #raw / 2
  local offset = #res
  for i = 1, words do
    local word = raw:sub(i * 2 - 1, i * 2)
    if byteswap then
      word = word:sub(2, 2) .. word:sub(1, 1)
    if wordswap then
      res[ offset + i ] = word
      res[ offset + 1 + words - i ] = word
  return true
local function readregisters(slaveid, fncode, data)
  if #data ~= 4 then
    return
  if count == 0 or count > limits.readregisters then
  if not map then
  local res = {}
  local max = count - 1
  while #res <= max do
    local mapobj = map[ addr + #res ]
    local success
    if mapobj then
      local value = grp.getvalue(mapobj.address)
      if type(value) == 'boolean' then
        value = value and 1 or 0
      if type(value) ~= 'number' then
        alert('invalid value ' .. mapobj.address .. ' ' .. tostring(value))
        value = 0
      success = readvalue(res, value, mapobj.dpt)
    if not success then
      res[ #res + 1 ] = zeroreg
  if #res ~= count then
  return string.char(count * 2) .. table.concat(res)
local function writevalue(obj, data, offset)
  local words = obj.len
  local len = words * 2
  local raw = data:sub(offset, offset + len - 1)
  if #raw < len then
    return
  local buf = {}
  for i = 1, words do
    local word = touint16(raw, i * 2 - 1, byteswap)
    local hex = string.format('%04X', word)
    if wordswap then
      buf[ #buf + 1 ] = hex
      table.insert(buf, 1, hex)
  local hexval = table.concat(buf)
  local dpt = obj.dpt
    dpt = f16float and dt.float32 or dt.int16
  local value = busdatatype.decode(hexval, dpt)
  if obj.dpt == dt.float16 and not f16float then
    value = value / f16mult
  _M.write(obj.address, value)
handlers.readcoils = readbits
handlers.readdiscreteinputs = readbits
handlers.readregisters = readregisters
handlers.readinputregisters = readregisters
handlers.writecoil = function(slaveid, fncode, data)
  if #data ~= 4 then
    return
  local bval = touint16(data, 3) == coilon
  _M.write(map[ addr ], bval, dt.bool)
  return data
  if #data ~= 4 then
    return
  return data
handlers.writecoils = function(slaveid, fncode, data)
  if #data < 5 then
    return
    return
  if count == 0 or count > limits.writebits or bytes ~= math.ceil(count / 8) then
  if not map then
  local offset = 6
  local byte = data:byte(offset)
  local bits = 0
    local bval = bit.band(bit.rshift(byte, bits), 1)
    if mapaddr then
      _M.write(mapaddr, bval, dt.bool)
    bits = bits + 1
    if bits == 8 then
      bits = 0
      offset = offset + 1
  if #data < 5 then
    return
    return
  if not map then
exception.tcp = function(sock, hdr, excode)
  local fncode = bit.bor(0x80, hdr:byte(8))
  local resp = hdr:sub(1, 4) ..
    string.char(0, 3) ..
    hdr:sub(7, 7) ..
    string.char(fncode, excode)
  return sock:send(resp)
exception.rtu = function(mbrtu, hdr, excode)
  local fncode = bit.bor(0x80, hdr:byte(2))
  local resp = hdr:sub(1, 1) ..
  return mbrtu:send(resp)
reply.tcp = function(sock, hdr, data)
    string.char(0, #data + 2) ..
    hdr:sub(7, 8) .. data
reply.rtu = function(mbrtu, hdr, data)
  local resp = hdr:sub(1, 2) .. data
local function handler(mode, ctx, hdr, data)
  local slaveid, fncode = hdr:byte(#hdr - 1, #hdr)
  local fnname = fncodes[ fncode ]
  if not fnname then
    return exception[ mode ](ctx, hdr, excodes.illegalfunction)
  local res = handlers[ fnname ](slaveid, fncode, data)
  if type(res) == 'number' then
    return exception[ mode ](ctx, hdr, res)
  elseif type(res) == 'string' then
    return reply[ mode ](ctx, hdr, res)
_M.tcphandler = function(sock)
  local hdr, err = sock:receive(8)
  if not hdr then
    return nil, err
  local len = touint16(hdr, 5) - 2
  local data
  if len <= 0 or len > maxpdu then
    err = 'protocol error'
    data, err = sock:receive(len)
  if not data then
    return nil, err
  return handler('tcp', sock, hdr, data)
_M.rtuhandler = function(mbrtu)
  local data, err = mbrtu:receive()
  if not data then
    return nil, err
  local slaveid = data:byte(1)
  if not mapping[ slaveid ] then
    return
  return handler('rtu', mbrtu, data:sub(1, 2), data:sub(3, #data - 2))
_M.setswap = function(swap)
  byteswap = swap:find('b') ~= nil
  wordswap = swap:find('w') ~= nil
_M.setfloat16precision = function(prec)
  prec = tonumber(prec) or 0
  f16mult = math.pow(10, prec)
_M.setfloat16mode = function(mode)
  f16float = mode == 'float'
  dtlens[ dt.float16 ] = f16float and 2 or 1
local function initobject(obj, dbobj)
  local dpt = obj.datatype or dbobj.datatype
  if type(dpt) == 'string' then
    dpt = dt[ dpt ] or 0
  if type(dpt) == 'number' and dpt >= 1000 then
    dpt = math.floor(dpt / 1000)
  obj.dpt = dpt
  obj.len = dtlens[ dpt ]
  obj.address = dbobj.address
  if not obj.len then
    alert('invalid data type ' .. obj.address .. ' ' .. tostring(dpt))
    return
  return obj
local function initobjects(objects)
  if type(objects) ~= 'table' then
    return
  for addr, obj in pairs(objects) do
    if type(obj) == 'string' then
      obj = { address = obj }
    local dbobj = grp.find(obj.address)
    if dbobj then
      obj = initobject(obj, dbobj)
      alert('missing object ' .. obj.address)
      obj = nil
    objects[ addr ] = obj
_M.write = grp.write
_M.setmapping = function(map)
  for _, smap in pairs(map) do
    initobjects(smap.registers)
    initobjects(smap.inputregisters)
  mapping = map
return _M
Resident script example:
mbrtu:open('/dev/RS485-1', 9600, 'E', 8, 1, 'H')
mbrtu:connect()
mbrtu:setslave('*') -- '*' handles multiple RTU slave IDs
mb.setswap('w')
mb.setmapping({
  [1] = {
    coils = {
      [0] = '0/0/1',
      [1] = '0/0/3',
      [2] = '0/0/4',
    discreteinputs = {
      [0] = '1/0/1',
      [1] = '1/0/3',
      [2] = '1/0/4',
    registers = {
      [0] = '1/1/4',
      [1] = '1/1/10',
      [3] = '32/1/6',
      [5] = '32/1/13',
    inputregisters = {
      [0] = '2/1/4',
      [1] = '2/1/10',
local gates = {
  ['0/0/3'] = '32/0/1',
  ['1/0/1'] = '32/0/2',
  ['1/0/3'] = '32/0/2',
  ['1/0/4'] = '32/0/3',
mb.write = function(addr, value, dt)
  local gate = gates[ addr ]
  if not gate or grp.getvalue(gate) then
    grp.write(addr, value, dt)
while true do
In gates table key (left side) is mapped group address and value (right side) is controlling gate object. Write to the given mapped group address will only happen if the gate value is true. Writing to group addresses without a gate group address is always allowed.
Hi, Thanks for sharing. It is working fine for the coils i.e 1 bit object. But we have holding registers as well that we are using for scene control in which we are sending 0,1 and 2 value from the same group address. How in the above script we can use gate function for the holding registers.
registers = {
      [1] = '6/3/6',
      [2] = '6/0/10',
      [3] = '6/0/11',
      [4] = '6/2/6',-
      [5] = '6/2/7',
gates table is shared, it works the same for coils and registers.