This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

modbus communcation error
#1
Hello everyone ! 
I face an issue with modbus commmunication with a heat pump. I atttach you the script and manual.
I checked it with the app "modbus polling", it works properly and I read data from the pump.

But via lm i have no communication.
Have you any idea about it ?

The json-profile:
{
    "manufacturer": "GREE",
    "description": "pump",
    "mapping": [
   
    {
    "name": "Water Tank Temperature",
    "datatype": "uint16",
    "type": "register",
    "address": 13,
    "unit": "°C"
    }
  ]
}

Attached Files
.pdf   Modbus Communication Protocol for Versati IV.pdf (Size: 1.84 MB / Downloads: 4)
Reply
#2
Start by using Read test, check wiring and correct RTU settings.
------------------------------
Ctrl+F5
Reply
#3
(27.08.2025, 09:50)Daniel Wrote: Start by using Read test, check wiring and correct RTU settings.

We have already done these steps, but no response.
The wiring and the rtu settings are correct.
Reply
#4
Did you try swapping A/B?
------------------------------
Ctrl+F5
Reply
#5
(27.08.2025, 10:11)Daniel Wrote: Did you try swapping A/B?

Yes, we tried but nothing changed.
We connected it to port 2 in the same LM and it works properly.
After that we changed LM and it works properly in port 1, because in this project we use port 2 for ekey.
So, the port 1 does not work in the first LM.
Reply
#6
OK then contact us via email for replacement.
------------------------------