Modbus SunSpec support
Does the modbus implementation in LM support the SunSpec Modbus Profile? I have an SMA invertor for my solar panels that I would like to query using the modbus protocol the parameters in attachment.
regards,
Joost
If the modbus bus is not proprietary the LM should be able to handle it.
You can try with this.
require('luamodbus') mb = luamodbus.rtu() mb:open('/dev/RS485', 19200, 'E', 8, 1, 'H') -- change with correct MB settings : speed, parity, stop bit, ... mb:connect() if mb ~= nil then     value = mb:readregisters(40188) -- read AC current register  log(value)     mb:close() end
The correct address is probably not 40188, but either 187 or 188. You can check this quickly with RTU test. If you want to create a profile, then address_scale field should be used to tell where to read the scaling factor from.