This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

can't get floor heating lua script to work on wiser
#1
hi, i got to this forum by googling and found a post about floor heating and virtual thermostat https://forum.logicmachine.net/showthrea...&pid=23068

i have 4 temp sensors (which show up correctly in the objects tab, data type is 09.001 2 bytes floating point) and a 6 way heating actuator (i can activate its channels by switching the channels value to true or false in the objects tab, data type is 01.002 boolean)


i added the floor heating widget and configured it like the following
https://imgur.com/a/RzpfwDe

i added a resident script with a 60s cycle and activated it

this is the script i came up with

--on/off widget status
statoonoff = grp.getvalue('32/1/4')
--write temperature to variable
tstudio = grp.getvalue('0/0/78')
--write widget setpoint temp to variable
settemp = grp.getvalue('32/1/3')
--check if the widget is enabled
if statoonoff==1 then
--check if setpoint is lower or greater in that room
if (settemp > tstudio) then
-- if setpoint is greater switch actuator channel on
grp.write('0/1/19', true)
else
--if setpoint is lower then switch actuactor channel off
grp.write('0/1/19', false)
end
--if widget is set to off turn off heating
else
grp.write('0/1/19', false)
end

the script isnt working, does anyone know whats wrong with it?
Reply
#2
32/1/4 is most likely boolean so this if does not work:
Code:
1
if (statoonoff == 1) then

It should be compared with true/false not 1/0. It can also be simply written like this:
Code:
1
if statoonoff then
Reply
#3
(10.11.2022, 12:13)admin Wrote: 32/1/4 is most likely boolean so this if does not work:
Code:
1
if (statoonoff == 1) then

It should be compared with true/false not 1/0. It can also be simply written like this:
Code:
1
if statoonoff then


32/1/4 was 01.001 data type, idk why it wasnt working. I changed it to 01.002 and used

if statoonoff

and its working, so thank you!!
Reply