This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

MODBUS - Can't write on registers
#1
Hi,

I created the attached modbus profiles for a fancoil. I CAN READ but I CAN'T WRITE on the holding registers (from 26301 to 26327).
What is wrong?

Thanks

Peppe

Attached Files
.json   IC-Radiantore - Inv.json (Size: 6.62 KB / Downloads: 13)
.pdf   XIST00073-Targa da incasso_rendition MODBUS.pdf (Size: 796.39 KB / Downloads: 8)
Reply
#2
Incorrect spelling: not writeble but writable
Reply
#3
Ooops.... that's embarassing! Smile
i did the fix, but i still can't write to the logs.
Yet with a modbus tool software I can write in the registers, but in the 0x10 mode: write multiple registers, as reported in the pdf manual.
Reply
#4
See this: https://forum.logicmachine.net/showthrea...e_multiple
Reply
#5
The script in the post - I suppose should be put as init script - refers to a tcp modbus connection... I have an RTU. re
And how I can map the registers to knx addresses?
Reply
#6
The suggestions is to use "write_multiple": 1 in your profile
------------------------------
Ctrl+F5
Reply
#7
(04.07.2023, 08:20)Daniel Wrote: The suggestions is to use "write_multiple": 1 in your profile

OK Thanks!
Reply