PID script
Hopefully someone can help me with the following "problem".
I would like to use the PID script to control the temperature in one of the bedrooms.
The temperature have to be set to 18 degrees... if under setpoint set groupadress ON, if setpoint reached set groupadress OFF.
I saw this example script, but the setpoint must not be an groupadress but a fixed value..
  1. -- init pid algorithm
  2. if not p then
  3.   p = PID:init({
  4.     current = '1/1/1',
  5.     setpoint = '18',
  6.     output = '1/1/3'
  7.   })
  8. end
  9.
  10. -- run algorithm
  11. p:run()
This script gives the following error:
Resident script:3: attempt to index global 'PID' (a nil value)
stack traceback:
So I think I made a mistake in the setpoint notation... can somebody help me?
Best,
Jos
You are probably missing the functions that are in the user lib, did you add these to user.pid?
To change the setpoint to a static value you probably need to change the function that gets the value from the object in user.pid, but i would advice to create a virtual object and just set the static value there once.
Next to that you also need require('user.pid') at the start of your script.
There is also a PID block in the FBEditor, maybe this one fits better to your needs.
Thanks Erwin,
I'm already a step further and it lookalike the scripts is working.
If I run the diagnostics inside ETS I see that the Logic machine sends an ON and OFF message to the group that has to turn the electrical radiator on... but nothing will happen....
The scripts that I'm using?
Do you have any idea why the group doesn't respond to the On and Off command? Do I have to set a datatype (switch?) somewhere?
-- init pid algorithm if not p then   p = PID:init({     current = '12/2/1',     setpoint = '32/1/1',     output = '12/0/7'   }) end -- run algorithm p:run()
Does all other bus communication works normal? My first reaction would be that the KNX interface is set to TCP/IP instead of TPUART.
All the scheduled scripts @ the Logic machine work fine.
Maybe you can see something @ the screen recording (see attachment)
Link to screen recording: https://www.dropbox.com/s/1n1o9me1vb3ku1...2.mov?dl=0
BTW... on the screen recording the script is off... Smile. That's not the issue Smile.
Can you check the script if it uses grp.update instead of grp.write?
grp.update sends to IP but not TP so you can see it on ETS monitor IP side but it’s not send to the TP, i guess that’s the issue you are facing.
From group monitor screenshot it looks like you have KNX TP/IP loop. Do you have any other IP interfaces connected to the same TP line?
(25.12.2019, 11:00)Erwin van der Zwart Wrote: Hi,
It uses grp.write... to be sure... this is the script
PID = {   -- default params   defaults = {     -- invert algorithm, used for cooling     inverted = false,     -- minimum output value     min = 0,     -- maximum output value     max = 100,     -- proportional gain     kp = 1,     -- integral gain     ki = 1,     -- derivative gain     kd = 1,   } } -- PID init, returns new PID object function PID:init(params)   local n = setmetatable({}, { __index = PID })   local k, v   -- set user parameters   n.params = params   -- copy parameters that are set by user   for k, v in pairs(PID.defaults) do     if n.params[ k ] == nil then       n.params[ k ] = v     end   end   -- reverse gains in inverted mode   if n.params.inverted then     n.params.kp = -n.params.kp     n.params.ki = -n.params.ki     n.params.kd = -n.params.kd   end   return n end -- resets algorithm on init or a switch back from manual mode function PID:reset()   -- previous value   self.previous = grp.getvalue(self.params.current)   -- reset iterm   self.iterm = 0   -- last running time   self.lasttime = os.time()   -- clamp iterm   self:clampiterm() end -- clamps iterm value function PID:clampiterm()   self.iterm = math.max(self.iterm, self.params.min)   self.iterm = math.min(self.iterm, self.params.max) end -- clamp and set new output value function PID:setoutput()   local t, object, value   self.output = math.max(self.output, self.params.min)   self.output = math.min(self.output, self.params.max)   value = math.floor(self.output)   local t = type(self.params.output)   -- write to output if object is set   if t == 'string' or t == 'table' then     if t == 'string' then       self.params.output = { self.params.output }     end     for _, output in ipairs(self.params.output) do       grp.write(output, value, dt.scale)     end   end end -- algorithm step, returns nil when disabled or no action is required, output value otherwise function PID:run()   local result   -- get manual mode status   local manual = self.params.manual and grp.getvalue(self.params.manual) or false   -- in manual mode, do nothing   if manual then     self.running = false   -- not in manual, check if reset is required after switching on   elseif not self.running then     self:reset()     self.running = true   end   -- compute new value if not in manual mode   if self.running then     -- get time between previous and current call     local now = os.time()     self.deltatime = now - self.lasttime     self.lasttime = now     -- run if previous call was at least 1 second ago     if self.deltatime > 0 then       result = self:compute()     end   end   return result end -- computes new output value function PID:compute()   local current, setpoint, deltasc, deltain, output   -- get input values   current = grp.getvalue(self.params.current)   setpoint = grp.getvalue(self.params.setpoint)   -- delta between setpoint and current   deltasc = setpoint - current   -- calculate new iterm   self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc   self:clampiterm()   -- delta between current and previous value   deltain = current - self.previous   -- calculate output value   self.output = self.params.kp * deltasc + self.iterm   self.output = self.output - self.params.kd / self.deltatime * deltain   -- write to output   self:setoutput()   -- save previous value   self.previous = current   return self.output end
(25.12.2019, 11:09)admin Wrote: From group monitor screenshot it looks like you have KNX TP/IP loop. Do you have any other IP interfaces connected to the same TP line?
Where can you see this? I'm using a Siemens Ip interface to connect ETS to the TP line. I only would use the logic machine to run scripts..
Can you help me what to change?
You don’t need to use the Siemens interface as the controller does the same functions, you can remove it. if you keep using it then disable KNX IP features in the KNX settings.
(25.12.2019, 16:13)Erwin van der Zwart Wrote: Hi,
check disabled the checkbox @ the logic machine.
Does it make sense that I have the address 1.1.100 for the logic machine?
Will check if the script is working fine now.
I see that the IP loop is gone Smile. not 4 messages anymore Smile.
But the Switch actor doesn't respond to the On or Off messages the logic machine is sending to group 12/0/7. (See attachment)
If I put A switch object from a taster in this group everything works fine...
(12.12.2019, 21:22)josdegroot Wrote: Hopefully someone can help me with the following "problem".
  2. if not p then
  3.   p = PID:init({
  5.     setpoint = '18',
  6.     output = '1/1/3'
  7.   })
  8. end
  9.
  11. p:run()
stack traceback:
Best,
Jos
hello,
I have the same problem with you and i don't know what to do to solve it.
Do you remember how you solved it?
Thank you
Add this to Common functions:
(10.06.2022, 12:54)admin Wrote: Add this to Common functions:
thank you for your answer,
after this i have the following error
"Common functions:331: attempt to perform arithmetic on local 'setpoint' (a nil value)
stack traceback:
Common functions:331: in function 'compute'
Common functions:315: in function 'run'
Check that setpoint object address is valid in the pid script.
(10.06.2022, 13:58)admin Wrote: Check that setpoint object address is valid in the pid script.
here is the script
  if not p then
    p = PID:init({
      current = '32/1/7',
      setpoint = '32/1/5',
      manual = '32/1/8',
      inverted = 0,
      output = '32/1/6',
      min=0,
      max=100,
      kp=1,
      ki=1,
      kd=1
  -- run algorithm
  p:run()
and the objects are shown in the attached
Restart the script via disable/enable. Also inverted should be false not 0. Because 0 evaluates as "true".
(10.06.2022, 14:12)admin Wrote: Restart the script via disable/enable. Also inverted should be false not 0. Because 0 evaluates as "true".
thank you very much,
Hello Admin,
I am trying to realize a constant light control loop with the PID script you have on the website.
I've tried to adjust the kp, ki, kd parameters to make the system stable but there are some issues.
Since this not about temperature control and fluctuations to the measured brightness value in the room can be pretty high due to sunny/cloudy day, the system is unstable. I would like to be able to set a min/max step (like +/- 3%) for the value that is written to the bus each control loop even if the PID calculation is resulting to a big difference from the previous value. In this way I would like to avoid positive or negative jumps in the written value. Another thing is to be able to add something like a deadband or hysteresis to the system so if the actual value = setpoint +/- 20 lux for exmple then don't calculate anything. Something similar of what is done now via the manual variable.
As my lua scripting skills are basic could you or anyone in this forum please help me figure this out and how the new script will be? Below I am attaching the script I am using now:
PID = {   -- default params   defaults = {     -- invert algorithm, used for cooling     inverted = false,     -- minimum output value     min = 10,     -- maximum output value     max = 100,     -- proportional gain     kp = 0.25,     -- integral gain     ki = 0.01,     -- derivative gain     kd = 0.1,   } } -- PID init, returns new PID object function PID:init(params)   local n = setmetatable({}, { __index = PID })   local k, v   -- set user parameters   n.params = params   -- copy parameters that are set by user   for k, v in pairs(PID.defaults) do     if n.params[ k ] == nil then       n.params[ k ] = v     end   end   -- reverse gains in inverted mode   if n.params.inverted then     n.params.kp = -n.params.kp     n.params.ki = -n.params.ki     n.params.kd = -n.params.kd   end   return n end -- resets algorithm on init or a switch back from manual mode function PID:reset()   -- previous value   self.previous = grp.getvalue(self.params.current)   -- reset iterm   self.iterm = 0   -- last running time   self.lasttime = os.time()   -- clamp iterm   self:clampiterm() end -- clamps iterm value function PID:clampiterm()   self.iterm = math.max(self.iterm, self.params.min)   self.iterm = math.min(self.iterm, self.params.max) end -- clamp and set new output value function PID:setoutput()   local t, object, value   self.output = math.max(self.output, self.params.min)   self.output = math.min(self.output, self.params.max)   value = math.floor(self.output)   local t = type(self.params.output)   -- write to output if object is set   if t == 'string' or t == 'table' then     if t == 'string' then       self.params.output = { self.params.output }     end     for _, output in ipairs(self.params.output) do       grp.write(output, value, dt.scale)     end   end end -- algorithm step, returns nil when disabled or no action is required, -- output value otherwise function PID:run()   local result   -- get manual mode status   local manual = false   if self.params.manual then     manual = grp.getvalue(self.params.manual)   end   -- in manual mode, do nothing   if manual then     self.running = false   -- not in manual, check if reset is required after switching on   elseif not self.running then     self:reset()     self.running = true   end   -- compute new value if not in manual mode   if self.running then     -- get time between previous and current call     local now = os.time()     self.deltatime = now - self.lasttime     self.lasttime = now     -- run if previous call was at least 1 second ago     if self.deltatime > 0 then       result = self:compute()     end   end   return result end -- computes new output value function PID:compute()   local current, setpoint, deltasc, deltain, output   -- get input values   current = grp.getvalue(self.params.current)   setpoint = grp.getvalue(self.params.setpoint)   -- delta between setpoint and current   deltasc = setpoint - current   -- calculate new iterm   self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc   self:clampiterm()   -- delta between current and previous value   deltain = current - self.previous   -- calculate output value   self.output = self.params.kp * deltasc + self.iterm   self.output = self.output - self.params.kd / self.deltatime * deltain   -- write to output   self:setoutput()   -- save previous value   self.previous = current   return self.output end
Thank you in advance.
Long time ago I worked on similar solution (not on LM) and to solve this we had to make lux more stable by making an avg form last few values. Try using something like this
https://forum.logicmachine.net/showthrea...1#pid27441