Belimo UK24MOD
Hi, have someone integrated uk24mod on LM5 ?
What does the script look like to extract the different values of knx?
I need to itegratedĀ 3 on each LM5.
https://www.belimo.eu/CH/EN/Product/Fire...&TopCatNr=
.pdf   UK24MOD_datasheet_en-gb.pdf (Size: 2.19 MB / Downloads: 16)
You don't need a script but a modbus profile. Which registers do you want to access apart from setpoint?
Here is a sampleĀ code after quick view on reference manual. Just to help you find a right way.
require('luamodbus') mb1 = luamodbus.rtu() -- RS-485 port name and number. here is RS485, but it can be RS485-1, RS485-2, ttyUSB0 -- connection parameters must to accord device settings mb1:open('/dev/RS485', 38400, 'E', 8, 1, 'H') mb1:connect() -- select modbus slave ID for read/write operations (55 here) mb1:setslave(55) --[[ read values we need to read hold register (command #3) modbus we can to assess: #1 - coil #2 - discrete input #3 - hold register #4 - input register ]]-- -- read all registers related to first MP i0, i1, i2, i3, i4, i5, i6, i7, i8, i9, i10, i11, i12, i13, i14, i15, i16, i17, i18, i19 = mb1:readregisters(0, 20) -- do something with this information -- set setpoint to 50 mb1:writeregisters(0, 50) mb1:close()
And my question to LM gurus: what will happens if there are device listed in 'ModBus' table located on the same RS485 bus. I assume that connection parameters are the same and there is no address conflict.
You should use a profile. If you want to use scripts and mapper on the same port then you need to use modbus proxy. See this for more info: https://forum.logicmachine.net/showthrea...53#pid1953
(18.11.2020, 12:24)admin Wrote: You don't need a script but a modbus profile. Which registers do you want to access apart from setpoint?
OK, I want access all. Is there a easy way to make modbus profile?
Here is profile documentation: https://openrb.com/docs/modbus.htm
Here are different examples: https://forum.logicmachine.net/showthread.php?tid=839
It is good practice to use RTU read test to check all parameters before creating the profile.
