Hi:
How can I Know that the bus KNX is disconnected outside Alerts. I want to send an email to know that situation.
Thanks.
Posts: 200
Threads: 60
Joined: Jun 2015
Reputation:
7
Hi,
So is there a way to do this? Is there a way to get specific alerts to generate an email?
Thanks,
Roger
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Yes, via a resident script:
Code: if not client then
function statushandler(status)
if status == 0x00 then
-- KNX Connected
elseif status == 0xFF then
-- KNX Disconnected
end
end
client = require('localbus').new(1)
client:sethandler('status', statushandler)
end
client:step()
Posts: 176
Threads: 42
Joined: Jul 2015
Reputation:
2
Good. Is there a way to fo the same with knx physical adresses as well? I was thinking to maybe ones a day run a script that checks programmed adresses and makes an alert if trouble and and ok message to the log if ok
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
There's knxlib.ping(phys_addr) function that you can use. But it will work only if your LM has direct KNX/TP connection.
Posts: 176
Threads: 42
Joined: Jul 2015
Reputation:
2
Ok. Thx. Yes i have tp so that will work
Posts: 200
Threads: 60
Joined: Jun 2015
Reputation:
7
(21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
Code: if not client then
function statushandler(status)
if status == 0x00 then
-- KNX Connected
elseif status == 0xFF then
-- KNX Disconnected
end
end
client = require('localbus').new(1)
client:sethandler('status', statushandler)
end
client:step()
Thank you. I added the function into the group address status script. From before.
Posts: 45
Threads: 14
Joined: Aug 2021
Reputation:
0
30.08.2021, 20:27
(This post was last modified: 31.08.2021, 05:46 by morkovka.)
(22.02.2017, 01:47)rocfusion Wrote: (21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
Code: if not client then
function statushandler(status)
if status == 0x00 then
-- KNX Connected
elseif status == 0xFF then
-- KNX Disconnected
end
end
client = require('localbus').new(1)
client:sethandler('status', statushandler)
end
client:step()
Thank you. I added the function into the group address status script. From before. I tried this function and it's not working in the current version of Wiser - does anyone have a current working version of this function to check the local KNX TP link?
Tried in a resident script and scheduled script (I prefer scheduled script), anyway the statushandler() function never gets called.
Thank you!
Morkov
Posts: 38
Threads: 2
Joined: Mar 2017
Reputation:
3
Hi,
I tested it with Wiser for KNX with firmware 2.6.2 and it was working for me.
You have to use resident script with sleep time 0.
(30.08.2021, 20:27)morkovka Wrote: (22.02.2017, 01:47)rocfusion Wrote: (21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
Code: if not client then
function statushandler(status)
if status == 0x00 then
-- KNX Connected
elseif status == 0xFF then
-- KNX Disconnected
end
end
client = require('localbus').new(1)
client:sethandler('status', statushandler)
end
client:step()
Thank you. I added the function into the group address status script. From before. I tried this function and it's not working in the current version of Wiser - does anyone have a current working version of this function to check the local KNX TP link?
Tried in a resident script and scheduled script (I prefer scheduled script), anyway the statushandler() function never gets called.
Best regards
forsterm
Posts: 45
Threads: 14
Joined: Aug 2021
Reputation:
0
Strange, I wonder what am I doing wrong.
I'm using this, in a resident script with sleep time 0:
Code: -- KNX TP connectivity check
function statushandler(status)
if status == 0x00 then
log('KNX connection check succesful')
elseif status == 0xFF then
alert('KNX is disconnected')
end
log('status is ' .. tostring(status))
end
client = require('localbus').new(1)
client:sethandler('status', statushandler)
client:step()
And I get nothing in the logs, error logs, alerts... any ideas?
(31.08.2021, 06:36)forsterm Wrote: Hi,
I tested it with Wiser for KNX with firmware 2.6.2 and it was working for me.
You have to use resident script with sleep time 0.
(30.08.2021, 20:27)morkovka Wrote: (22.02.2017, 01:47)rocfusion Wrote: (21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
Code: if not client then
function statushandler(status)
if status == 0x00 then
-- KNX Connected
elseif status == 0xFF then
-- KNX Disconnected
end
end
client = require('localbus').new(1)
client:sethandler('status', statushandler)
end
client:step()
Thank you. I added the function into the group address status script. From before. I tried this function and it's not working in the current version of Wiser - does anyone have a current working version of this function to check the local KNX TP link?
Tried in a resident script and scheduled script (I prefer scheduled script), anyway the statushandler() function never gets called.
Thank you!
Morkov
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
You won't get any log until the connection status changes. If you want to get the current status the use status = buslib.isconnected()
Posts: 45
Threads: 14
Joined: Aug 2021
Reputation:
0
(31.08.2021, 07:53)admin Wrote: You won't get any log until the connection status changes. If you want to get the current status the use status = buslib.isconnected()
Thank you, that works well!
What's the difference between 'knxlib' and 'buslib'?
Thank you!
Morkov
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
No difference, both variables reference the same library functions
Posts: 88
Threads: 15
Joined: Sep 2019
Reputation:
1
What can be the reason for KNX / TP disconnected messages?
In my alerts, I have many messages from KNX / TP connected and KNX / TP disconnected, but I do not know why.
Thanks.
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Which hardware version do you have?
Posts: 88
Threads: 15
Joined: Sep 2019
Reputation:
1
HW: LM5 Lite (i.MX6)
SW: 20200703
Posts: 45
Threads: 14
Joined: Aug 2021
Reputation:
0
I also experience this, once every few days - in the Error log I see:
Quote:KNX/TP: Transmitter Error (send 0 receive 1)
And in the Alerts log, at the same exact time (same second), it says:
Quote:KNX/TP: Connected
Using W4K i.MX6.
Thank you!
Morkov
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Transmitter error and temperature warning usually means that there are too many devices on the KNX line.
Posts: 45
Threads: 14
Joined: Aug 2021
Reputation:
0
(01.10.2021, 14:06)admin Wrote: Transmitter error and temperature warning usually means that there are too many devices on the KNX line.
What temperature warning? I don't see it.
Just the transmitter error coupled with a 'connected' (as if the device's KNX line was disconnected and reconnected)
Thank you!
Morkov
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Temperature warning is another indication of an overloaded line. It's not guaranteed to appear though. The more devices are on the KNX line the harder it is to transmit data. This leads to the chip overheating and/or not being able to transmit at all (send 0 receive 1 error).
|