convert percentage to 3 digital outputs
I would like to convert a numeric (percentage) to 3 digital outputs (group addresses). For example i want to make the first DO to be 1 when the percentage is between 5-30%, the second between 35-70% and the third between 75-100%.
I want this to control o fcu.
Is there any idea how to do this.
Thank you
You have gaps between 30..35 and 70..75. Is this intended? Do you want to have hysteresis between these values?
i have gaps, because i want to ensure that the digital outputs will never be energized simultaneously.
Hysterisis is a good idea.
Hi, is that what you need?
percent_val = event.getvalue() -- your value --the first 5-30%, the second between 35-70% and the third between 75-100%. first_obj = '5/0/1' -- address of first object second_obj = '5/0/2' -- address of second object third_obj = '5/0/3'  -- address of third object if(percent_val >= 0 and percent_val < 5) then -- turn off   grp.write(first_obj, 0) -- first object set to 0   grp.write(second_obj, 0) -- second object set to 0   grp.write(third_obj, 0) -- third object set to 0 elseif( percent_val >= 5 and percent_val <= 30 ) then   grp.write(first_obj, 1) -- first object set to 1   grp.write(second_obj, 0) -- second object set to 0   grp.write(third_obj, 0) -- third object set to 0 elseif( percent_val >= 35 and percent_val <= 70 ) then   grp.write(first_obj, 0)   grp.write(second_obj, 1)   grp.write(third_obj, 0) elseif( percent_val >= 75 and percent_val <= 100 ) then   grp.write(first_obj, 0)   grp.write(second_obj, 0)   grp.write(third_obj, 1) end
I would improve this a bit as now you can have (shortly) 2 high contacts..
First write to false before writing anything to true (5-30% and 35-70% are not doing that)
Even a better way to do this is to have a “switch on” delay in the ETS application so you have a second pauze before a contact is closed.
Erwin van der Zwart, thank you for your feedback.
percent_val = event.getvalue() -- your value --the first 5-30%, the second between 35-70% and the third between 75-100%. first_obj = '5/0/1' -- address of first object second_obj = '5/0/2' -- address of second object third_obj = '5/0/3'  -- address of third object if(percent_val >= 0 and percent_val < 5) then -- turn off   grp.write(first_obj, 0) -- first object set to 0   grp.write(second_obj, 0) -- second object set to 0   grp.write(third_obj, 0) -- third object set to 0 elseif( percent_val >= 5 and percent_val <= 30 ) then   grp.write(second_obj, 0) -- second object set to 0   grp.write(third_obj, 0) -- third object set to 0   os.sleep(1) -- delay to do not have two objects on simultaneously   grp.write(first_obj, 1) -- first object set to 1 elseif( percent_val >= 35 and percent_val <= 70 ) then   grp.write(first_obj, 0)   grp.write(third_obj, 0)   os.sleep(1)   grp.write(second_obj, 1) elseif( percent_val >= 75 and percent_val <= 100 ) then   grp.write(first_obj, 0)   grp.write(second_obj, 0)   os.sleep(1)   grp.write(third_obj, 1) end
I would not use os.sleep in this script as you can have weird behavior when the input value is changed within a second (script can run in paralell), use 1 second “on delay” in the application of your actuator.
It should be fine if the % value probably comes from a PID script where control value is sent every X seconds.
