This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus help
#1
When using LM5 for Modbus communication, if the resident script queries the register status while the event script is writing to the register, it may not be possible to write to the register. How can this be better resolved?
Reply
#2
Use profiles.
Reply
#3
(22.04.2026, 09:36)admin Wrote: Use profiles.

Are there any examples for reference?
Reply
#4
Profiler app: https://forum.logicmachine.net/showthread.php?tid=5911
Profile reference: https://kb.logicmachine.net/misc/modbus-profile/
Profile examples: https://forum.logicmachine.net/showthread.php?tid=839
Reply
#5
I use a JSON file to map MODBUS. At first, I couldn't actively read it; it could only automatically send values to KNX when they changed. Is there any solution?
Reply
#6
What do you mean by "actively read it"? In Modbus device settings you specify poll interval - all registers that are mapped to group addresses will be read every X seconds. Mapped group address values will be updated if the Modbus value differs from the current value.
Reply