Alert message function
Dear All,
I would like to write an alert everytime temperature is >= a setpoint.
I can use event base script or resident script but in both case alert message will appear everytime the temperature change or every base time set as resident script.
I would like to log alert only when temperature surpasses set point for the first time and not going on to send alert message. If temperature remains above set point for 1 day alert must be only 1.
What do you suggest?
You can compare current temperature with setpoint in temperature event-based script, but you must keep last value(or threshold) in storage. And when the temperature exceed the threshold then you can send some alert.
Map event script to temperature value, change 1/1/1 to setpoint object address:
temperature = event.getvalue() setpoint = grp.getvalue('1/1/1') alerted = storage.get('alerted') if temperature >= setpoint then   if not alerted then     alert('temperature is above setpoint')     storage.set('alerted', true)   end else   storage.set('alerted', false) end
How can I activate a sound on the screen with an object = 1 and deactivate with an object = 0
You can use custom JS like this sample: https://forum.logicmachine.net/showthrea...20#pid7920
Or you the alert manager app.