Posts: 185
Threads: 38
Joined: Feb 2017
Reputation:
3
(01.10.2017, 14:57)Erwin van der Zwart Wrote: Hi,
Yes you could do it but this option is depending on your received dataset, i checked yours but in this dataset you got back it's givving you timeframes of 6 hours, so you cant use that, i would search for a more detailed weather API ..
BR,
Erwin
OK, any idea of where I can get it?
Also, so I learn a little more, how do you see that it is a dataset for 6 hours? I just used the one posted earlier in this thread, so I am not really sure how it works.
Trond
There are 10 kinds of people in the world; those who can read binary and those who don't
Posts: 1746
Threads: 6
Joined: Jul 2015
Reputation:
115
01.10.2017, 17:11
(This post was last modified: 02.10.2017, 07:08 by Erwin van der Zwart.)
Hi,
Just paste the url from the request in your browser, there you see the original XML structure.
For better API you could try something like this as it has real time forecast and hourly data http://www.apixu.com (or any other of the 1000 available), another plus is that it also has JSON data so you don't need the XML parser to get a LUA table. You can use this free if you don’t need interval faster then 10 minutes (= max 5000 calls a month)
Here is a sample to get data from the apixu api:
Code: require 'ssl.https'
require 'json'
-- Set your API key here
api_key = 'xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx'
-- Set here your location
location = 'Amsterdam'
-- Request data from API
r,c,h,s = ssl.https.request('https://api.apixu.com/v1/forecast.json?key=' .. api_key .. '=' .. location)
-- Decode JSON data to LUA table
if r then
result = json.pdecode(r)
else
alert('Could not fetch data')
return
end
-- Get next hour temperature
temperature_in_one_hour = result['forecast']['forecastday'][1]['hour'][1]['temp_c']
-- Do something with the received temperature
log(temperature_in_one_hour)
I'm not sure hour 1 is next hour or 1:00 so maybe you need to add small algorithm to compare with 'now' and selected day / hour from the table
BR,
Erwin
Posts: 86
Threads: 10
Joined: Jul 2015
Reputation:
1
Happy new year to all.
I think that the Weather service has stoped working since some days ago. Can you please check this?
Thank you in advance.
Posts: 408
Threads: 102
Joined: Oct 2016
Reputation:
9
Hi
Yes. I can confirm it stopped working 4.1.2019.
http://openrb.com/weather/?w=796597
returns
{"error":true,"cause":"response error"}
LM5Lp, firmware: 2018.08.22 and 2021.12.15, FlashSYS v2, ARMv7 Processor rev 5 (v7l), kernel 4.4.151 and 4.4.259
Posts: 17
Threads: 3
Joined: May 2017
Reputation:
0
Hi.
There´s some changes in the Yahoo API.
They changed the link and created a user key system (like OpenWeatherMap) that is needed for get the data.
BR
Posts: 135
Threads: 23
Joined: May 2017
Reputation:
2
Posts: 408
Threads: 102
Joined: Oct 2016
Reputation:
9
Is there somebodybody who has a ready solution for yr.no?
https://api.met.no/
https://api.met.no/weatherapi/documentation
It looks easy, doesn't require autentication token etc. SoI'm asking before I'm going to implement it.
LM5Lp, firmware: 2018.08.22 and 2021.12.15, FlashSYS v2, ARMv7 Processor rev 5 (v7l), kernel 4.4.151 and 4.4.259
Posts: 7309
Threads: 41
Joined: Jun 2015
Reputation:
419
See this example for yr.no: https://forum.logicmachine.net/showthrea...64#pid1164
As for Yahoo, we are still waiting for them to accept our access request since their API changed again.
Posts: 408
Threads: 102
Joined: Oct 2016
Reputation:
9
Thank you Admin
If someone is interested in then there's yrno script below (warning: uses obsolete API)
Function minmax_temp_tomorrow returns lowest and highest temperature for tomorrow. The script is simple and ignores time shift.
Code: require('socket.http')
forecast = {}
function parsetag(parser, tag, attributes)
if tag == 'time' then
table.insert(forecast, {})
forecast[ #forecast ].from=attributes.from
forecast[ #forecast ].to=attributes.to
forecast[ #forecast ].period=attributes.period
elseif tag == 'symbol' then
forecast[ #forecast ].symbol = attributes.name
elseif tag == 'precipitation' then
forecast[ #forecast ].precipitation = attributes.value
elseif tag == 'windDirection' then
forecast[ #forecast ].wind_direction = attributes.code
elseif tag == 'windSpeed' then
forecast[ #forecast ].wind_speed = attributes.mps
elseif tag == 'temperature' then
forecast[ #forecast ].temperature = attributes.value
elseif tag == 'pressure' then
forecast[ #forecast ].pressure = attributes.value
end
end
function yrno_fetch()
local url = 'http://www.yr.no/place/Czech_Republic/Prague/Prague/varsel.xml'
local data, err = socket.http.request(url)
if data then
require('lxp').new({
StartElement = parsetag
}):parse(data)
else
alert('Fetch failed: ' .. tostring(err))
end
end
function minmax_temp_tomorrow()
local ld_minTemp
local ld_maxTemp
local next_day={}
yrno_fetch()
if (not forecast) then
return
end
local ll_tomorrow=os.time()+24*3600 -- tomorrow as long
local lt_tomorrow= os.date("*t",ll_tomorrow) -- tomorrow as table for use if forecast_write
--gets date of tomorrow
local ls_match=os.date("%Y--%m--%d",ll_tomorrow)
for index, value in ipairs(forecast) do
if (value.from:match("^"..ls_match)) then
local ld_temp=tonumber(value.temperature)
if (ld_minTemp == nil) then
ld_minTemp=ld_temp
end
if (ld_maxTemp == nil) then
ld_maxTemp=ld_temp
end
if (ld_temp<ld_minTemp or index==1) then
ld_minTemp=ld_temp
end
if (ld_temp>ld_maxTemp or index==1) then
ld_maxTemp=ld_temp
end
end
end
return ld_minTemp,ld_maxTemp,lt_tomorrow
end
LM5Lp, firmware: 2018.08.22 and 2021.12.15, FlashSYS v2, ARMv7 Processor rev 5 (v7l), kernel 4.4.151 and 4.4.259
Posts: 120
Threads: 24
Joined: Jul 2015
Reputation:
0
(08.01.2019, 16:21)Thomas Wrote: Thank you Admin
If someone is interested in then there's yrno script below (warning: uses obsolete API)
Function minmax_temp_tomorrow returns lowest and highest temperature for tomorrow. The script is simple and ignores time shift.
Code: require('socket.http')
forecast = {}
function parsetag(parser, tag, attributes)
if tag == 'time' then
table.insert(forecast, {})
forecast[ #forecast ].from=attributes.from
forecast[ #forecast ].to=attributes.to
forecast[ #forecast ].period=attributes.period
elseif tag == 'symbol' then
forecast[ #forecast ].symbol = attributes.name
elseif tag == 'precipitation' then
forecast[ #forecast ].precipitation = attributes.value
elseif tag == 'windDirection' then
forecast[ #forecast ].wind_direction = attributes.code
elseif tag == 'windSpeed' then
forecast[ #forecast ].wind_speed = attributes.mps
elseif tag == 'temperature' then
forecast[ #forecast ].temperature = attributes.value
elseif tag == 'pressure' then
forecast[ #forecast ].pressure = attributes.value
end
end
function yrno_fetch()
local url = 'http://www.yr.no/place/Czech_Republic/Prague/Prague/varsel.xml'
local data, err = socket.http.request(url)
if data then
require('lxp').new({
StartElement = parsetag
}):parse(data)
else
alert('Fetch failed: ' .. tostring(err))
end
end
function minmax_temp_tomorrow()
local ld_minTemp
local ld_maxTemp
local next_day={}
yrno_fetch()
if (not forecast) then
return
end
local ll_tomorrow=os.time()+24*3600 -- tomorrow as long
local lt_tomorrow= os.date("*t",ll_tomorrow) -- tomorrow as table for use if forecast_write
--gets date of tomorrow
local ls_match=os.date("%Y--%m--%d",ll_tomorrow)
for index, value in ipairs(forecast) do
if (value.from:match("^"..ls_match)) then
local ld_temp=tonumber(value.temperature)
if (ld_minTemp == nil) then
ld_minTemp=ld_temp
end
if (ld_maxTemp == nil) then
ld_maxTemp=ld_temp
end
if (ld_temp<ld_minTemp or index==1) then
ld_minTemp=ld_temp
end
if (ld_temp>ld_maxTemp or index==1) then
ld_maxTemp=ld_temp
end
end
end
return ld_minTemp,ld_maxTemp,lt_tomorrow
end
Hi Thomas,
Do you have an example of how to write the forecast to GA? and what datatype the different object needs to be?
BR Even Sundgot.
Posts: 408
Threads: 102
Joined: Oct 2016
Reputation:
9
Hi
1. I stored the script above in library ecl_yrno (don't forget to change URL according to your location)
2. I added script below into my scheduler. You have to change GAs to addresses you use in your project.
7/2/30 and 7/2/31 are 9.001 (temperature, float)
7/2/32 is 11.3 (date)
Code: function forecast_write(low,high,next_day)
low = low or 0
high = high or 0
next_day = next_day or 0
grp.write('7/2/30', low, dt.float16)
grp.write('7/2/31', high, dt.float16)
grp.write('7/2/32', next_day, dt.date)
end
require ('user.ecl_yrno')
forecast_write(minmax_temp_tomorrow())
LM5Lp, firmware: 2018.08.22 and 2021.12.15, FlashSYS v2, ARMv7 Processor rev 5 (v7l), kernel 4.4.151 and 4.4.259
Posts: 86
Threads: 10
Joined: Jul 2015
Reputation:
1
(08.01.2019, 14:46)admin Wrote: As for Yahoo, we are still waiting for them to accept our access request since their API changed again.
Hi, any news or estimations from Yahoo regarding when you will have access to repair the existing weather service?
Posts: 7309
Threads: 41
Joined: Jun 2015
Reputation:
419
No response from them, we will probably have to move to a more reliable data provider.
Posts: 7309
Threads: 41
Joined: Jun 2015
Reputation:
419
Since there's no response from Yahoo we suggest using https://apixu.com instead. You will have to create a free account and make sure that your script does not fetch data too quickly (not less than once in 5 minutes).
Here's a short example, change key variable to your API key, location variable to required location in textual form. This example fetches current weather condition and forecast for today and tomorrow. Fields can be found in apixu documentation: https://www.apixu.com/doc/forecast.aspx (day Element).
Code: require('json')
https = require('ssl.https')
escape = require('socket.url').escape
key = 'my_api_key'
location = 'my location name'
url = 'https://api.apixu.com/v1/forecast.json?key=%s&q=%s&days=2'
url = string.format(url, key, escape(location))
res = https.request(url)
data = json.pdecode(res)
if type(data) ~= 'table' then
alert('failed to load weather data')
return
end
if data.error then
log('error', data.error)
return
end
current = data.current
today = data.forecast.forecastday[ 1 ].day
tomorrow = data.forecast.forecastday[ 2 ].day
-- log(current, today, tomorrow)
-- temperature in C
grp.write('32/1/1', current.temp_c)
-- "feels like" temperature in C
grp.write('32/1/2', current.feelslike_c)
-- humidity as percentage
grp.write('32/1/3', current.humidity)
-- wind speed in kilometers per hour
grp.write('32/1/4', current.wind_kph)
-- uv index
grp.write('32/1/5', current.uv)
-- weather condition text
grp.write('32/1/6', current.condition.text)
-- pressure in millibars
grp.write('32/1/7', current.pressure_mb)
-- precipitation amount in millimeters
grp.write('32/1/8', current.precip_mm)
-- minimum temperature in celsius for the day
grp.write('32/2/1', today.mintemp_c)
-- maximum temperature in celsius for the day
grp.write('32/2/2', today.maxtemp_c)
-- average temperature in celsius for the day
grp.write('32/2/3', today.avgtemp_c)
-- average humidity as percentage
grp.write('32/2/4', today.avghumidity)
-- maximum wind speed in kilometers per hour
grp.write('32/2/5', today.maxwind_kph)
-- uv index
grp.write('32/2/6', today.uv)
-- weather condition text
grp.write('32/2/7', today.condition.text)
-- total precipitation in millimeters
grp.write('32/2/8', today.totalprecip_mm)
-- minimum temperature in celsius for the day
grp.write('32/3/1', tomorrow.mintemp_c)
-- maximum temperature in celsius for the day
grp.write('32/3/2', tomorrow.maxtemp_c)
-- average temperature in celsius for the day
grp.write('32/3/3', tomorrow.avgtemp_c)
-- average humidity as percentage
grp.write('32/3/4', tomorrow.avghumidity)
-- maximum wind speed in kilometers per hour
grp.write('32/3/5', tomorrow.maxwind_kph)
-- uv index
grp.write('32/3/6', tomorrow.uv)
-- weather condition text
grp.write('32/3/7', tomorrow.condition.text)
-- total precipitation in millimeters
grp.write('32/3/8', tomorrow.totalprecip_mm)
Posts: 15
Threads: 4
Joined: May 2017
Reputation:
0
(30.03.2016, 10:45)admin Wrote: Another option is to use forecast from http://yr.no
You have to replace URL with the one that corresponds to your location.
Code: require('socket.http')
forecast = {}
function parsetag(parser, tag, attributes)
if tag == 'time' then
table.insert(forecast, {})
elseif tag == 'symbol' then
forecast[ #forecast ].symbol = attributes.name
elseif tag == 'precipitation' then
forecast[ #forecast ].precipitation = attributes.value
elseif tag == 'windDirection' then
forecast[ #forecast ].wind_direction = attributes.code
elseif tag == 'windSpeed' then
forecast[ #forecast ].wind_speed = attributes.mps
elseif tag == 'temperature' then
forecast[ #forecast ].temperature = attributes.value
elseif tag == 'pressure' then
forecast[ #forecast ].pressure = attributes.value
end
end
url = 'http://www.yr.no/place/United_Kingdom/England/London/varsel.xml'
data, err = socket.http.request(url)
if data then
require('lxp').new({
StartElement = parsetag
}):parse(data)
log(forecast)
else
alert('Fetch failed: ' .. tostring(err))
end
Hi!
This works fine when im checking the log but how do I modify it to write the values to bus?
Best Regards!
P
Posts: 4188
Threads: 21
Joined: Aug 2017
Reputation:
175
Hi
I'm doing it like that
Code: require('socket.http')
forecast = {}
function parsetag(parser, tag, attributes)
if tag == 'time' then
table.insert(forecast, {})
elseif tag == 'symbol' then
forecast[ #forecast ].symbol = attributes.name
elseif tag == 'precipitation' then
forecast[ #forecast ].precipitation = attributes.value
elseif tag == 'windDirection' then
forecast[ #forecast ].wind_direction = attributes.code
elseif tag == 'windSpeed' then
forecast[ #forecast ].wind_speed = attributes.mps
elseif tag == 'temperature' then
forecast[ #forecast ].temperature = attributes.value
elseif tag == 'pressure' then
forecast[ #forecast ].pressure = attributes.value
end
end
url = 'http://www.yr.no/place/United_Kingdom/England/Farnborough/varsel.xml'
data, err = socket.http.request(url)
if data then
require('lxp').new({
StartElement = parsetag
}):parse(data)
grp.update('Weather precipitation', tonumber(forecast[1].precipitation))
grp.update('Weather symbol', forecast[1].symbol)
grp.update('Weather windDirection', forecast[1].wind_direction)
grp.update('Weather windSpeed', tonumber(forecast[1].wind_speed))
grp.update('Weather temperature', tonumber(forecast[1].temperature))
grp.update('Weather pressure', tonumber(forecast[1].pressure))
--log(forecast)
else
alert('Fetch failed: ' .. tostring(err))
end
------------------------------
Ctrl+F5
Posts: 135
Threads: 23
Joined: May 2017
Reputation:
2
18.01.2019, 16:16
(This post was last modified: 18.01.2019, 16:23 by balatis.)
(18.01.2019, 07:50)admin Wrote: Since there's no response from Yahoo we suggest using https://apixu.com instead. You will have to create a free account and make sure that your script does not fetch data too quickly (not less than once in 5 minutes).
Here's a short example, change key variable to your API key, location variable to required location in textual form. This example fetches current weather condition and forecast for today and tomorrow. Fields can be found in apixu documentation: https://www.apixu.com/doc/forecast.aspx (day Element).
Code: require('json')
https = require('ssl.https')
escape = require('socket.url').escape
key = 'my_api_key'
location = 'my location name'
url = 'https://api.apixu.com/v1/forecast.json?key=%s&q=%s&days=2'
url = string.format(url, key, escape(location))
res = https.request(url)
data = json.pdecode(res)
if type(data) ~= 'table' then
alert('failed to load weather data')
return
end
if data.error then
log('error', data.error)
return
end
current = data.current
today = data.forecast.forecastday[ 1 ].day
tomorrow = data.forecast.forecastday[ 2 ].day
-- log(current, today, tomorrow)
-- temperature in C
grp.write('32/1/1', current.temp_c)
-- "feels like" temperature in C
grp.write('32/1/2', current.feelslike_c)
-- humidity as percentage
grp.write('32/1/3', current.humidity)
-- wind speed in kilometers per hour
grp.write('32/1/4', current.wind_kph)
-- uv index
grp.write('32/1/5', current.uv)
-- weather condition text
grp.write('32/1/6', current.condition.text)
-- pressure in millibars
grp.write('32/1/7', current.pressure_mb)
-- precipitation amount in millimeters
grp.write('32/1/8', current.precip_mm)
-- minimum temperature in celsius for the day
grp.write('32/2/1', today.mintemp_c)
-- maximum temperature in celsius for the day
grp.write('32/2/2', today.maxtemp_c)
-- average temperature in celsius for the day
grp.write('32/2/3', today.avgtemp_c)
-- average humidity as percentage
grp.write('32/2/4', today.avghumidity)
-- maximum wind speed in kilometers per hour
grp.write('32/2/5', today.maxwind_kph)
-- uv index
grp.write('32/2/6', today.uv)
-- weather condition text
grp.write('32/2/7', today.condition.text)
-- total precipitation in millimeters
grp.write('32/2/8', today.totalprecip_mm)
-- minimum temperature in celsius for the day
grp.write('32/3/1', tomorrow.mintemp_c)
-- maximum temperature in celsius for the day
grp.write('32/3/2', tomorrow.maxtemp_c)
-- average temperature in celsius for the day
grp.write('32/3/3', tomorrow.avgtemp_c)
-- average humidity as percentage
grp.write('32/3/4', tomorrow.avghumidity)
-- maximum wind speed in kilometers per hour
grp.write('32/3/5', tomorrow.maxwind_kph)
-- uv index
grp.write('32/3/6', tomorrow.uv)
-- weather condition text
grp.write('32/3/7', tomorrow.condition.text)
-- total precipitation in millimeters
grp.write('32/3/8', tomorrow.totalprecip_mm)
hi
for me do not work where is the fault?
thanks in advance.
////////////
require('json')
https = require('ssl.https')
escape = require('socket.url').escape
key = 'dd14841bec7c428a8ed154420191801'
location = 'https://www.apixu.com/weather/q/patra-west-greece-greece-2855484'
url = 'https://api.apixu.com/v1/forecast.json?key=%s&q=%s&days=2'
url = string.format(url, key, escape(location))
res = https.request(url)
data = json.pdecode(res)
if type(data) ~= 'table' then
alert('failed to load weather data')
return
end
if data.error then
log('error', data.error)
return
end
current = data.current
today = data.forecast.forecastday[ 1 ].day
tomorrow = data.forecast.forecastday[ 2 ].day
-- log(current, today, tomorrow)
-- temperature in C
grp.write('32/1/1', current.temp_c)
-- "feels like" temperature in C
grp.write('32/1/2', current.feelslike_c)
-- humidity as percentage
grp.write('32/1/3', current.humidity)
-- wind speed in kilometers per hour
grp.write('32/1/4', current.wind_kph)
-- uv index
grp.write('32/1/5', current.uv)
-- weather condition text
grp.write('32/1/6', current.condition.text)
-- pressure in millibars
grp.write('32/1/7', current.pressure_mb)
-- precipitation amount in millimeters
grp.write('32/1/8', current.precip_mm)
-- minimum temperature in celsius for the day
grp.write('32/2/1', today.mintemp_c)
-- maximum temperature in celsius for the day
grp.write('32/2/2', today.maxtemp_c)
-- average temperature in celsius for the day
grp.write('32/2/3', today.avgtemp_c)
-- average humidity as percentage
grp.write('32/2/4', today.avghumidity)
-- maximum wind speed in kilometers per hour
grp.write('32/2/5', today.maxwind_kph)
-- uv index
grp.write('32/2/6', today.uv)
-- weather condition text
grp.write('32/2/7', today.condition.text)
-- total precipitation in millimeters
grp.write('32/2/8', today.totalprecip_mm)
-- minimum temperature in celsius for the day
grp.write('32/3/1', tomorrow.mintemp_c)
-- maximum temperature in celsius for the day
grp.write('32/3/2', tomorrow.maxtemp_c)
-- average temperature in celsius for the day
grp.write('32/3/3', tomorrow.avgtemp_c)
-- average humidity as percentage
grp.write('32/3/4', tomorrow.avghumidity)
-- maximum wind speed in kilometers per hour
grp.write('32/3/5', tomorrow.maxwind_kph)
-- uv index
grp.write('32/3/6', tomorrow.uv)
-- weather condition text
grp.write('32/3/7', tomorrow.condition.text)
-- total precipitation in millimeters
grp.write('32/3/8', tomorrow.totalprecip_mm)
how is possible to put in visu a widget weather like this?
Posts: 7309
Threads: 41
Joined: Jun 2015
Reputation:
419
Try this:
Code: location = 'patra, greece'
For widget you will need to create a separate html page, upload it via ftp and then display by using iframe element.
Posts: 135
Threads: 23
Joined: May 2017
Reputation:
2
(18.01.2019, 16:31)admin Wrote: Try this:
Code: location = 'patra, greece'
For widget you will need to create a separate html page, upload it via ftp and then display by using iframe element.
Thanks admin
can i have information for sunset and sunrise.
Posts: 7309
Threads: 41
Joined: Jun 2015
Reputation:
419
Use this for sunrise/sunset. Object data type must be set to text/string.
Code: astro = data.forecast.forecastday[ 1 ].astro
grp.write('32/4/1', astro.sunrise)
grp.write('32/4/2', astro.sunset)
grp.write('32/4/3', astro.moonrise)
grp.write('32/4/4', astro.moonset)
You can also use built-in rscalc function for this: https://forum.logicmachine.net/showthread.php?tid=1010
|