(18.05.2023, 12:21)Daniel Wrote: By default they are all connected via multicast. Create same object in both and see if value is updated after change.
I already EXPORT object from #1SpaceLYnk to #2SpaceLYnk, but value dont changed (value change just in main SpaceLYnk)
All FILTERS are disabled ('no filter').
Multicast addresses are the same.
I also changed TTL from 1 to 5..6.. etc (there are about 5switches/routers between KNX routers)
The IT service claims that everything is fine with them.
Therefore, I want to prove that they did not create something correctly. But how?