This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

GCHV Modbus to LM5
#1
           
Guys, I have problem with GCHV modBus Gateway I have write the script however I can't write
can you please check it . ??

Code:
{
  "manufacturer": "GCHV",
  "description": "test",
  "mapping": [
      {
      "name": "On Off",
      "address": 40003,
      "value_custom": {
        "1": "Off",
        "2": "On"
          },
      "bus_datatype": "float32",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0XC000",
  "writable": true,
      "write_bitmask": true
    },
      {
      "name": "Setting tempreture",
      "address": 40003,
      "bus_datatype": "temperature",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0X001F",
  "writable": true,
      "write_bitmask": true
    },
{
      "name": "Fan speed",
      "address": 40003,
      "value_custom": {
        "1": "low spped",
        "2": "middle spped",
        "4": "high speed",
        "8": "Auto speed(low speed for GEN3+)"
      },
      "bus_datatype": "uint8",
      "datatype": "uint8",
      "type": "register",
  "value_bitmask": "0X01E0",
  "writable": true,
      "write_bitmask": true
    },
{
      "name": "setting mode",
      "address": 40003,
      "value_custom": {
        "1": "cooling mode",
        "2": "dehumidification mode (cooling mode for GEN3+)",
        "4": "Ventilation mode",
        "8": "heating mode",
        "16": "AUTO mode(cooling mode for GEN3+)",
        "9": "floor heating",
        "10": "intelligent floor heating"
      },
      "bus_datatype": "uint8",
      "datatype": "uint16",
      "type": "register",
  "value_bitmask": "0X3E00",
  "writable": true,
      "write_bitmask": true
    }
  ]
}

Attached Files
.xlsx   NEW MODBUS TABLE.xlsx (Size: 40.33 KB / Downloads: 3)
Reply


Messages In This Thread
GCHV Modbus to LM5 - by Samer - 24.11.2023, 10:25
RE: GCHV Modbus to LM5 - by admin - 24.11.2023, 10:35
RE: GCHV Modbus to LM5 - by Samer - 24.11.2023, 11:03
RE: GCHV Modbus to LM5 - by admin - 24.11.2023, 11:03
RE: GCHV Modbus to LM5 - by Samer - 24.11.2023, 11:04
RE: GCHV Modbus to LM5 - by admin - 24.11.2023, 11:05
RE: GCHV Modbus to LM5 - by Samer - 24.11.2023, 14:17
RE: GCHV Modbus to LM5 - by admin - 24.11.2023, 14:20

Forum Jump: